      I'm getting to grips with my AT1 VFD… it's mounted in a wall cabinet, with buttons mounted on the lid. I have set the parameters the way I want, and all is going well, except for:

      P53 (X4) set to 18, jog reverse. Nothing happens. I can select reverse, then press 'jog forward', which does work – just no 'jog reverse'. I'd rather not have reverse available as my lathe spindle has a threaded mount and I'd rather not have the chuck unwinding itself onto the lathe bed if I accidentally leave it in reverse!

      P54 (X5) set to 19, emergency stop. I have a latching 'mushroom' button on the lid. Again, nothing happens when pressed, and the motor continues to run. At the moment I have set it to 16, 'external error' which does the job – but not ideal.

      I have checked the operation of the buttons with a multimeter, and they're doing what they're supposed to do.

      Can anyone give me some clues?

      Cheers,

      David

      Advert
      #28644
      David Jenkins 4
      Participant
        @davidjenkins4
        #592103
        David Jenkins 4
        Participant
          @davidjenkins4

          Oops!

          Left out some vital info… this is the manual for the VFD: http://myosuploads3.banggood.com/products/20190919/20190919015909SKU792664.pdf

          It's probably the smallest unit, at 1/2 HP (I'm using it with a 1/3 HP motor).

           

          Edited By David Jenkins 4 on 30/03/2022 20:18:10

          #592109
          An Other
          Participant
            @another21905

            Don't know if I'm reading this correctly, but according to the manual, multifunctional Input 1 (P58) apparently must be set to 20 to enable multifunction inputs P50 to 55, but by default it is set to 0.

            #592114
            David Jenkins 4
            Participant
              @davidjenkins4

              Not sure – other functions are working, such as Start, Stop, Emergency stop (in the dodgy error-forcing way I've implemented it), Jog and Error Reset. All without setting P58.

              P58/SP1 is one of the most obscure parts of the instructions – the parameter tables call it "Multi function input", but in the diagram it's shown as "Open collector output". In my opinion, it's a method for switching something external by pulling this terminal down to 0v, e.g. an external relay or an indication light. If so, it gives no idea of the current carrying ability! (my guess is 'minimal' ). This probably is operated by option 20 from the control inputs. Note that the next one, P60/SP2 (not available on the very basic AT1) is described as 'relay output'.

              Saying that, I might try it, just for the hell of it!

              However I could be totally wrong – it's horribly ambiguous – like most of the 'manual'! I have decades of experience in electrics and electronics, but this manual is a farce. The value of the product would go up 100% if the manual was re-written sensibly.

              I do have something that works, and (I believe) installed safely, but I just want it to work properly, "to the book".

              Edited By David Jenkins 4 on 30/03/2022 20:58:49

              #592617
              iNf
              Participant
                @inf

                David

                Is your emergency stop latching button NO or NC ?

                NC do work but only on release when they remake the circuit in the normal stop modes, so might be the same on the e-stop?

                #592622
                noel shelley
                Participant
                  @noelshelley55608

                  Yep ! My thoughts, is the stop button NC or NO, then there's the issue of latching ! Noel

                  #592623
                  David Jenkins 4
                  Participant
                    @davidjenkins4

                    My switch has both NC and NO available – I'm using the NO side.

                    In other words – the contacts are open when not pressed, then closed and latched when pressed. They continue to be closed until the mushroom button is twisted and released. I did set one of the other NO buttons to 19, and it still doesn't work (I held the button in!).

                    It looks as though option 19 simply doesn't work on any of the X1 – X6 inputs… I'm going to leave it as 16, "external error", as at least that works (it also proves that the switch is working correctly). At least it deactivates the system until the VFD is reset.

                    #592625
                    peak4
                    Participant
                      @peak4

                      Glad it's not just me that's struggling with this one.
                      I can't get E-Stop to work either, and tried it with various X posts, and both NO & NC switches.

                      At the moment I'm using momentary NO push buttons for start/stop, and a latching toggle for reverse, with all parameters at default except;

                      P10 – 2 External Speed
                      P11 – 2 External on/off
                      P50 – 3 X1 Start
                      P51 – 4 X2 Stop
                      P52 – 5 X3 Reverse
                      P25 – 1 1425 rpm

                      I've tried playing with P58 and P50 for E-Stop and failed there
                      P53 – 19 doesn't work either for E-Stop.

                      In my case, I don't need jog at the moment, as it's for a tapping machine (Reverse, is in case I ever need to do any left hand tapping.

                      Bill

                      #592628
                      iNf
                      Participant
                        @inf

                        When bench testing I found the emergency stop option 19 in p50-55 had the same effect as option 0 (inertial stop ) in p12 or the same as when the power is cut and the motor just slowly spools down, not what you really want for an e-stop frown

                        Option 1 (deceleration stop) in p12 stops reasonably quickly and certainly quicker than my ml7 single phase lathe.

                        Option 2 (brake stop ) certainly stops quickly but would be quite mechanically unsympathetic if used constantly, though playing around with braking time/ voltage in p13/14 may help, I haven't tried that.

                        I have just acquired a Harrison m250 lathe and wanted to use the original controls as far as possible.

                        I have :

                        P50-x1 set to 3 NO momentary switch= start

                        P51-x2 set to 4 NO momentary switch = stop ( keeping the stop pressed in has no effect and pressing start will start the motor and you have to release the stop button and re-press to stop )

                        P52-x3 set to 9 wire reversing on the original rotary switch reverse

                        P52-x4 set to 15 section speed input 3 on the original rotary switch forward. This is for a slow forward set speed but could be programed in p29 for any frequency.

                        When the rotary switch is in the centre original off position, pressing start ,starts the lathe in forward, switching to original reverse, reverses and original forward gives slow forward without having to switch the lathe off. The stop p51- x2 works in all these positions and in the event of losing power, on restarting the vfd the lathe doesn't run until start is pressed.

                         

                        Edited By iNf on 02/04/2022 23:18:41

                        #640884
                        fraser polhill
                        Participant
                          @fraserpolhill91784

                          I am using this VFD on a horizontal mill, I want to use the relay output to enable the coolant pump. Any idea what parameter controls the function of the output to make when running?

                          #640889
                          Martin Connelly
                          Participant
                            @martinconnelly55370

                            From the standard AT1, AT2, AT3 data sheet. TA common, TB Normally open, TC normally closed. 250VAC 5A/30VDC 3A

                            You will have to check with a multi-meter if this is triggered by starting the motor and stopping the motor.

                            Martin C

                            PS The data sheet shows the relay as optional. Out of curiosity I searched for images of the terminals. There are a few showing TA, TB and TC as solder pads on the board next to the UVW outputs. You will have to investigate for yourself if these are connected to a relay and need either wires soldering to them or a small socket/plug needs adding.

                            Edited By Martin Connelly on 11/04/2023 13:37:24

                            #774626
                            matildo
                            Participant
                              @matildo

                              Hello, i did some tests and i discovered its posible to manipulate emergency stop setting P.50=19, if you read the manual it enables X1 as an emergency stop input. Normally it has 12v so you have to put a switch between X1 and COM from the VFD pinout so it can be set to 0v for sending the stop signal.

                              About P.58 is the sp1 output, for example if you want to detect a failure juts have to set P.58=3 then check with you multimeter when and error shows, for example Err2 on VFD display, the voltaje between SP1 and COM goes from 12v to 0v.

                              My VFD has the pinout for TA, TB, and TC (Relay outputs) Even checked with a multimeter continuity between TA and TB, and open circuit between TA and TC as the manual diagram says. But i cant find a way to activate the relay. For exmple open circuit on TA and TB when a VDF failure shown on VFD display like Err 2. Any thoughts are welcome, thanks.

                            Viewing 13 posts - 1 through 13 (of 13 total)
                            • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                            Advert

                            Latest Replies

                            Home Forums General Questions Topics

                            Viewing 25 topics - 1 through 25 (of 25 total)
                            Viewing 25 topics - 1 through 25 (of 25 total)

                            View full reply list.

                            Advert

                            Newsletter Sign-up