        Does anyone have any experience of installing a Yaskawa VFD. The fuse protection seems a bit illogical and a bit over the top. The unit draws 11 to 13.5 amp but the installation book specifies either a 40 amp non time delay fuse or a 80 amp time delayed fuse. These seem to be american type fuses. Being a spanner and not a sparks I would have just used a 16 amp mcb. I have asked my local electical supplier but he has no experience with VFD’s. Has anyone any suggestions?
        Peter

        #293215
        Andy Holdaway
        Participant
          @andyholdaway

          Not sure what model or Kw rating your VFD is, but based on your current consumption figures I would go with a 16 or 20 amp Type C MCB or RCCBO.

          Andy

          #293216
          Emgee
          Participant
            @emgee

            Hi Peter

            A lot depends on how you start the motor, either ramp up slowly or go for max rpm to start in the shortest time possible, the 40A fuse is only 3xflc so could well do the job in both cases. Check the installation book or the markings on the unit to establish max rating fuse allowed for protection, keep below that rating.

            Emgee

            #293219
            Clive Foster
            Participant
              @clivefoster55965

              With a VFD the worst case demand is the switch on surge to charge the capacitor bank providing the DC supply that the VFD chops up to generate 3 phase AC. If you happen to switch on at just the right point in the incoming AC cycle you get a very large inrush current for, relatively speaking, quite a long time. Enough to take out a quick blow fuse unless its very overrated relative to the nominal steady state draw.

              Ages since I had owt to do with this sort of thing but I think worst case switch on point is around 150 volts.

              Ideally the switch on should be remote via a relay and zero crossing detector so the actual switch is at zero volts letting the capacitor voltage rise alongside the AC input rather than trying to jump from 0 to a high voltage. Fuse suggestions imply that your inverter is direct switch on not zero voltage controlled.

              Clive.

              #293226
              KWIL
              Participant
                @kwil

                Agree with Andrew Holdaway, my Yaskowa VFD is OK on a 15A MCB

                #293229
                Emgee
                Participant
                  @emgee
                  Posted by KWIL on 13/04/2017 14:17:09:

                  Agree with Andrew Holdaway, my Yaskowa VFD is OK on a 15A MCB

                  One that I sold recently needed a 32A type D mcb to hold on when switching the unit on but that was supplying more current to the bigger motor.

                  Emgee

                  #293230
                  Martin Connelly
                  Participant
                    @martinconnelly55370

                    I can't remember what size mcb I have in the supply line for my workshop but occasionally when I switch on one of the VFDs I have the mcb trips. It is only about 1% to 2% of the time and I usually switch it on before anything else apart from the lights so it is a slight annoyance only. It must be if I switch it on at the worst possible point in the ac cycle. Once on the mcb has never tripped in use.

                    Martin C

                    #293254
                    Martin Connelly
                    Participant
                      @martinconnelly55370

                      Have checked the mcb and it is 32A. It does supply other things as well as the workshop.

                      Martin C

                      #293351
                      Peter Parker
                      Participant
                        @peterparker23659

                        Thanks everyone for your answers to my post.

                        I don't think I gave enough info on the problem.

                        The Yaskawa unit I am using is a J1000 Model CIMRJCBA0006BAA

                        The input is 220v 1phase 11 to 13.5 amp

                        The output is 220v 3phase 1.1 Kw 6 amp

                        The motor that I have fitted to my Colchester Bantam is a Compton Series 10 inverter compliant , 3phase 1.1Kw 4.8 amp @50Hz 1400 rpm..

                        The installation guide is gobbledygook to me. It specifies some very expensive time delay and non time delay fuses from 30 amp to 80 amp. Yaskawa said to stick to the installation guide as what is specified has been tested to work, so no help there. My local electrical supplier is a very experience electrical engineer but has no experience of VFD's.

                        Regards Peter

                        Edited By Peter Parker on 14/04/2017 13:44:50

                        #293357
                        Muzzer
                        Participant
                          @muzzer

                          That's only a 0.75kW / 1hp drive, so I can't imagine what business you'd have fitting anything like the ratings you are talking about.

                          VFDs have a soft start circuit to limit inrush current (there are regulations that require it to be limited as you might expect), so talk of silly big currents at turn on is plain unhelpful.

                          Perhaps you could link to the relevant page in the spec or paste a screenshot.

                          Murray

                          PS I'll be installing a 3.3kW Yaskawa VFD later this weekend, so may have some more insight to offer then.

                          I see from the installation manual that the fuse ratings you mention are for compliance with UL / cUL ie for industrial installations in America and Canada. The fuse ratings are somehting like 3 times the rated input current. You should ignore them. These drives are something like 97-98% efficient, so the input power isn't going to significantly differ from the output power. Don't overthink this!

                          Edited By Muzzer on 14/04/2017 14:46:05

                          #293360
                          KWIL
                          Participant
                            @kwil

                            Murray, its on page 251 of the Yaskawa Guide and is to do with meeting UL.

                            Red herring, The only confusion in installing these VFDs is finding the right page in the manual!

                            #407145
                            john fletcher 1
                            Participant
                              @johnfletcher1

                              I have a Yaskawa VS mini J7 series inverter, some kind person "here" helped me out when I was unable to get a slow speed, they pointed me in the right direction enabling me to alter an item in the program. Now I would like to increase the top speed from 2000rpm to 3000rpm.which item is it please. John

                              #407163
                              Pete Rimmer
                              Participant
                                @peterimmer30576

                                I have several machines with vfd up to 2.2kw and all of them are fitted with a 3 pin plug and 13 app fuse. None have ever blown the fuse nor tripped the 32a mcb in the panel.

                                #407174
                                SillyOldDuffer
                                Moderator
                                  @sillyoldduffer

                                  Bit of a guess, but I think what's going on is the manufacturer is recommending the best possible fuse for a particular set of circumstances:

                                  1. On power up the VFD capacitor bank might draw a short burst of very heavy current if the switch happens to be operated close to the top of the AC cycle. To the supply it will look like a short except it only lasts a few milliseconds. This is worst case, if by luck the switch is turned on 10mS earlier, the voltage will be zero, and current starts to flow gently. 5mS after the peak and the voltage is well on the way down. I feel this is less likely to happen with modern VFD because it's not difficult to design in zero point starting. BUT
                                  2. The motor pulls a lot of extra current on start-up, especially if it's already loaded and the lubrication is stiff on a cold day. Again the supply 'sees' something suspiciously like a short circuit except it doesn't last long.

                                  Given there are two false short-circuits how best to defend against a dangerous real short? One way is to fit a slow blow fuse sized to the expected 'normal' current; these take a heavy current for long enough not to be fooled by brief overloads. But each time it happens the fuse is stressed and it will give up the ghost eventually: as a solution it's safe but causes interruptions. Alternatively, fit a fuse large enough to take the full short-term overload current plus a little extra, but make sure it has a fast blow characteristic. A big quick blow fuse will be resilient to brief overloads but can be sized to pop quickly in the event of an actual fault.

                                  In amateur use an ordinary 13A fuse should be fine. The VFD is unlikely to be powered up and down as much as a professional set-up, and the ordinary fuse may last decades. Eventually it might get tired and die, but that's hardly a crisis – just put a new one in. This approach wouldn't do in a professional shop and the VFD supplier would get complaints. To avoid them, I suggest he recommends an expensive fuse that balances safety and reliability. All we need to is keep it safe.

                                  I'm reasonably comfortable using a small fuse in place of a big one. What would be a gigantic mistake would be to replace the makers recommended expensive fast blow fuse with an nice cheap slow blow of the same amperage. A lot more damage will be done in the time it takes a slow-blow to eventually break.

                                  Ignore any and all of the above if a professional electrician disagrees!

                                  Dave

                                  #407184
                                  Mike Poole
                                  Participant
                                    @mikepoole82104
                                    Posted by john fletcher 1 on 30/04/2019 09:13:42:

                                    I have a Yaskawa VS mini J7 series inverter, some kind person "here" helped me out when I was unable to get a slow speed, they pointed me in the right direction enabling me to alter an item in the program. Now I would like to increase the top speed from 2000rpm to 3000rpm.which item is it please. John

                                    Parameter 09 set to 100hz would be a start, this would give a synchronous speed of 3000rpm which in reality because of slip will be about 2850rpm for a four pole motor, if the motor plate rates the motor at about 1450rpm at 50hz then you have a four pole motor. If you want to get an actual 3000rpm then you will need to raise the 100hz a bit more. You will be working in the constant power area of the drive so you will lose torque. The motor and bearings will usually be fairly happy at double its design speed, what about the machine you are driving? If it is a lathe check the headstock bearing will be happy and the max speed of any chucks you fit, this is in the comfort zone of most chucks but you should check.

                                    Mike

                                    Edited By Mike Poole on 30/04/2019 16:40:33

                                    #407200
                                    john fletcher 1
                                    Participant
                                      @johnfletcher1

                                      Thank you Mike, I will check things on Thursday. The motor is a 4 pole type and is fitted to my bench top Naerok mill.. I've had the mill almost 30 years and don't remember any critical comments about Korean products like I frequently hear regarding model engineering items from China.,strange old World. At the time I was mighty glad to get what I have, the casting finish ought to have been better, but it given me a lot of pleasure. John

                                    Viewing 17 posts - 1 through 17 (of 17 total)
                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                    Advert

                                    Latest Replies

                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                    View full reply list.

                                    Advert

                                    Newsletter Sign-up