My central heating is working at last !!
Faults were:
Boiler overheating and tripping the overheat cut-out.
Air leak in the positive pressure sensing system in the boiler, preventing it from firing up.
Blockage in another part of the air pressure sensing system, ditto.
Damaged flue gasket.
Main board failure – re soldered all connections, but that did not fix it. No circuit diagrams or even schematics available and did not have the time to trace the circuit out myself. New main board.
No restrictor fitted to the hot water loop, so if HW was selected on as well as the CH, the HW would steal the hot water from the boiler and the radiators would stay cold.
Magnetite detected, (with a magnet), in some pipe junctions. This caused blockages which were preventing fill water from the expansion tank in the loft getting into the system, and restricting the flow of water through the system.
Cut out the affected pipework and fitted new pipe, including fitting a restrictor valve in the hot water loop.
All back together, with cleaner fluid circulating and radiators all balanced.
A warm house after 2 weeks of very low temperatures in the house – down to 8°C at one point.
Total cost, about £100 for a new control board and cleaning solution.
BUT………on clearing up, the sheet I had carefully put down on the carpet by the airing cupboard before starting work turned out to be porous and the light coloured carpet is stained. So another £100 to have the carpet cleaned.