The normal idea when paralleling two or more alternator sets, was that one was the master and was isochronous governed, while the other(s) were slave and droop governed.
Ideally, they were all in sync and no circulating currents happened (Lamp out).
Parallelling with an infinite bus, (mains) was an interesting activity.
Some multiple sets incorporated relays which would isolate a slave set, if the circulating currents were too large.
Many years ago, at Southdown Central Works, there were three 1000 rpm alternators, powered by Gardner 5LWs which had been removed from buses and the governor arms extended to tighten the governing so that they would hold a constant speed at 1,000 rpm. The idea was to save money, during winter, by powering the lights from the alternators rather than the mains.
The governing was too tight to be stable and damping was minimal, so the attendant spent all winter afternoons frantically trying to keep the lamps out; and failing. They just flickered on and off in sequence while he juggled the controls.
In another completely different context, I was unpopular with Woodward Governor Company for slugging a droop governor so that it did not try to govern out torsional vibrations!
They had spent thousands of dollars to develop a speedy response, and I was damping it heavily, to slow the response; hence the unhappiness!
An engine capable of a high instantaneous rate of acceleration could very difficult to control with a droop governor, to get a steady speed; especially if the selected speed was near to peak torque speed.
But an isochronous governor was more expensive, so droop was the first choice, where possible.
Howard