Posted by John W1 on 08/11/2015 12:09:26:
"We use a heat store for hot water so there is no run up time as there is with combi's"
The run up time is going to be the same regardless of what you have at the boiler end. It's due to the column of water standing in the pipes between it and the tap. Not only do you have to flush the cool water out but you also have to bring the copper pipework up to temp before full temp is achieved. Our Worcester Bosch combi heat exchanger was kept at temperature at all times and the full 30kW output was available through the hot water outlet if required.
The only way to avoid run up time is to have a circulating hot water system. In these, the hot water runs around a circuit rather like CH. When you turn the tap on, hot water is almost instantly available. Of course the downside is that you are constantly incurring heat loss from the whole circuit which is why they tend to be found in very high end properties.
In my view, the main downside of the combi system was the tendency of the control loop to fight the thermostatic shower valves – and the radiator TRVs fighting with the room thermostat (eg at my mother's house). With a system fitted with TRVs, it makes little sense to have a room thermostat and as mentioned it can actually cause conflict (boiler overtemp protection).
Murray