  • #303155
    Tony Pratt 1
    Participant
      @tonypratt1

      Thanks one & all, plenty of good advice to mull over.

      Tony

      Advert
      #303168
      SillyOldDuffer
      Moderator
        @sillyoldduffer
        Posted by Michael Gilligan on 19/06/2017 07:40:44:

        Posted by Tony Pratt 1 on 19/06/2017 07:22:19:

        Hi Guys,

        I can hear a massive amount of buzzing on the radio.

        Tony

        VFD basically synthesise their "sinewave" so it looks something like this: **LINK**

        MichaelG.

        That's right, but the waveforms aren't so neat in the real world. Just for interest, here's some screenshots of the waveform output by my VFD on dead slow.

        p4wv.jpg

        As you can see the waveform is a very rough approximation of a 50 Hz sine-wave.

        Zooming in on the detail reveals how it's been built up

        p3wv.jpg

        p2wv.jpgp1wv.jpg

        basicwv.jpg

        The 50Hz 'sine wave' seen by the motor is synthesised from a 10kHz square wave. Square waves are wonderfully efficient because the semiconductor switches inside the VFD are either fully on or fully off, which means they don't get hot. But those very fast on-off transitions create radio frequency energy. While DC and AC tend to stay with the cable RF has no such limitation. Rapidly alternating currents produce mutually supporting electric and magnetic fields that expand to infinity. Although most of the power produced by a VFD behaves like 50Hz AC, a proportion of it is RF that will radiate if it can. A good way to stop it is with earthed metal shields and perhaps a filter..

        Sharp spikes produced by VFDs might cause grief inside older motors (pre 1980, allegedly). Although most old 3 phase induction motors 'just work', there are reports on the web of insulation failures and unwanted currents flowing in the bearings.

        RF currents produce counter-intuitive effects. If, for example, you connect a 50Hz power source to the base of a large air-cored inductor, nothing much happens. A 100kHz power source connected to the same coil will produce spectacular effects like a Tesla Coil. A Tesla coil can be made by accident. If your motor/VFD combination starts producing big sparks, suspect a loose connection. It's important to fix it quickly; although RF created voltages are unlikely to cause much damage in themselves, they can start an arc that ordinary AC will sustain with thoroughly bad results.

        Dave

        Edit: checked it twice and still didn't see the typos before hitting save.

        Edited By SillyOldDuffer on 19/06/2017 13:50:23

        #303171
        Anonymous
          Posted by SillyOldDuffer on 19/06/2017 13:46:40:

          While DC and AC tend to stay with the cable RF has no such limitation. Rapidly alternating currents produce mutually supporting electric and magnetic fields that expand to infinity. Although most of the power produced by a VFD behaves like 50Hz AC, a proportion of it is RF that will radiate if it can. A good way to stop it is with earthed metal shields and perhaps a filter.

          By definition an RF signal is AC. They're one and the same thing, not different things. Any AC signal will radiate an electromagnetic wave, unless of course Maxwell got it wrong.

          I'm afraid you're getting confused about Tesla coils. They are a resonant transformer, not a coil as such, and it is the Q of the resonant circuits, and the step up ratio, that allows very high voltages to be generated.

          By the way the waveform you 'see' from the output of the VFD will depend upon whether you measure phase to phase or phase to 'neutral'.

          Andrew

          #303194
          SillyOldDuffer
          Moderator
            @sillyoldduffer
            Posted by Andrew Johnston on 19/06/2017 14:16:19:

            Posted by SillyOldDuffer on 19/06/2017 13:46:40:

            While DC and AC tend to stay with the cable RF has no such limitation. Rapidly alternating currents produce mutually supporting electric and magnetic fields that expand to infinity. Although most of the power produced by a VFD behaves like 50Hz AC, a proportion of it is RF that will radiate if it can. A good way to stop it is with earthed metal shields and perhaps a filter.

            By definition an RF signal is AC. They're one and the same thing, not different things. Any AC signal will radiate an electromagnetic wave, unless of course Maxwell got it wrong.

            I'm afraid you're getting confused about Tesla coils. They are a resonant transformer, not a coil as such, and it is the Q of the resonant circuits, and the step up ratio, that allows very high voltages to be generated.

            By the way the waveform you 'see' from the output of the VFD will depend upon whether you measure phase to phase or phase to 'neutral'.

            Andrew

            Yup. True that AC is RF, I have no argument with Maxwell.

            What I was trying to say was that the tendency for a wire to radiate is much lower at 50Hz than at radio frequencies. An efficient antenna (half-wave dipole) at 50Hz would be 3000km long. In comparison domestic electrical wiring is much too short and close to the ground to radiate much. Radio Frequency AC is not nearly so constrained, an efficient transmitting antenna at 30MHz being only 5 metres long. Light is also AC and that doesn't behave much like 50Hz electricity at all.

            Though I understand Tesla Coils to my own satisfaction I plead guilty to confusing everyone else. I started by saying 'like a Tesla Coil', meaning only that shoving a spike of energy into an inductor is liable to up the voltage at the other end. But then I said 'A Tesla coil can be made by accident' which is definitely misleading. You're right, the way a car ignition coil makes volts is not quite the same as a transformer, nor the same as a resonant transformer. I still suggest that: odd things happen when RF is about.

            Good point about looking at the waveforms phase to phase, which is what the motor actually gets as input. I'd have put my oscilloscope across two of the phases except I couldn't think of a quick way of doing it without accidentally shorting one of them to earth. It's too hot for that kind of excitement today.

            Thanks for helping me clarify.

            Dave

            Edit , typos…

            Edited By SillyOldDuffer on 19/06/2017 15:21:07

            #303197
            Howard Lewis
            Participant
              @howardlewis46836

              Being concerned that my invertor did not back radiate any unpleasant RF into the mains (did not want to mess up anything in our house or any other house connected to the same phase), I fed it through a (secondhand) suppressed mains socket. After nearly fourteen years, there seem to have been no problems.

              This is UK, running off a 13 Amp 240 volt socket, 50 Hertz, with the feed coming from the house through a RCD.

              Elsewhere in the world, things may be different.

              Howard

              #303384
              Lee Goulding
              Participant
                @leegoulding74917

                some picture of the Star wiring that i need to make Mesh/Delta so i can then connect the Inverter which i believe connects from U,V,W to any of ABC on the motor.

                Any helps would be great

                Thanks

                img_5454.jpg

                #303391
                John Rudd
                Participant
                  @johnrudd16576

                  Need a better picture…..

                  If that is a Star wired motor, you need the star point accessing to change to Delta….

                  What motor is it?

                  There are threads on here giving advice in how to change from Star to Delta…

                  #303400
                  Lee Goulding
                  Participant
                    @leegoulding74917

                    Hi John

                    i have seen a few posts on it but no simple explanations i.e remove all wires and connect Colour/Wire to A,B,C,N etc

                    The white cable in the picture is going to the electrical control unit on the lathe itself so i presume that will be disconnected altogether and the remaining wires i are to the motor which then need connecting Brown to A, White to B and Black to C with nothing on N to make it Mesh/Delta

                    Thanks

                    img_5389.jpg

                    img_5456.jpg

                    Edited By Lee Goulding on 20/06/2017 15:32:44

                    #303428
                    Neil Wyatt
                    Moderator
                      @neilwyatt
                      Posted by Muzzer on 18/06/2017 21:11:54:

                      6dB is actually a factor of 2, given that we are talking about voltages. For power, 6dB would be a factor of 4 (= 2 squared).

                      The heat is getting to you!

                      Murray

                      He was talking about loudness actually… which can be interpreted as voltage or power but is neither.

                      Neil;

                      #303429
                      Neil Wyatt
                      Moderator
                        @neilwyatt

                        You can set the carrier frequency of an IMO Cub anywhere between 0.75 and 15Khz, which should provide a way of reducing any interference left after improving the screening to avoid your favourite radio station (or target the one your neighbour listens to).

                        Do read the manual on the pros and cons cf changing the frequency:

                        Lowering the carrier frequency increases the ripple components (harmonic
                        components) on the output current waveform so as to increase the
                        motor's power loss and raises the temperature of the motor. If the carrier
                        frequency is set at 0.75 kHz, for example, estimate the motor output
                        torque at 85% or less of the rated motor torque.
                        On the contrary, raising the carrier frequency increases the inverter’s
                        power loss and raises the temperature of the inverter. The inverter has a
                        built-in overload protection function that automatically decreases the
                        carrier frequency to protect the inverter. For details about the function,
                        refer to function code H98.

                        #303431
                        Neil Wyatt
                        Moderator
                          @neilwyatt

                          Posted by SillyOldDuffer on 19/06/2017 13:46:40:

                          If your motor/VFD combination starts producing big sparks, suspect a loose connection.

                          See the video someone posted a while ago who thought they had a bad VFD, showing exactly this behaviour.

                          N.

                          #303435
                          John Rudd
                          Participant
                            @johnrudd16576

                            Lee,

                            I am totally confused……

                            The white cable is connected to your motor's terminals marked A,B and C, yes or no?

                            Is the machine currently running from a 3 phase supply or not?

                            You want to run from a single phase supply using an inverter?

                            Connected to the motor's terminals A,B,C and N, there are coloured wires as per the photo depicting Star…..?

                            #303443
                            Lee Goulding
                            Participant
                              @leegoulding74917

                              Hi

                              Yes the cable is connected to ABC

                              The machine was running from a phase before it came to me

                              Yes it will be run from an inverter with Pendent for control

                              Yes it looks as though it's in Star

                              Thanks

                              #303447
                              John Rudd
                              Participant
                                @johnrudd16576

                                In that case, connect the coloured motor wires as per the diagram, for Mesh, then use the White cable ( if its long enough..) connecting to terminals U,V and W on the inverter, the free end to terminals A,B and C on your motor.

                                There should be no wires connected to the N terminal.

                                Edited By John Rudd on 20/06/2017 19:00:01

                                #303448
                                Lee Goulding
                                Participant
                                  @leegoulding74917

                                  Hi John

                                  Ok thanks for that will do but I'm going to replace the white cable with some SY shielded cable as it's not long enough

                                  Thanks

                                  #303485
                                  Anonymous
                                    Posted by SillyOldDuffer on 19/06/2017 15:19:20:

                                    Good point about looking at the waveforms phase to phase, which is what the motor actually gets as input. I'd have put my oscilloscope across two of the phases except I couldn't think of a quick way of doing it without accidentally shorting one of them to earth.

                                    You need one of these:

                                    differential_probe.jpg

                                    ….a differential probe. Essentially the potential divider is split on either side of the measurement resistor. So the ground of the 'scope' may be connected to ground on the EUT but through many megaohms, so not a problem.

                                    I bought mine to look at gate drive and output signals on high current (2500A) half bridges running from rectified three phase.

                                    Andrew

                                    #303490
                                    Mike Poole
                                    Participant
                                      @mikepoole82104

                                      You could let the scope float by disconnecting the earth, to indicate the earth was disconnected we used to have a long earth and pull it out of the plug top so you could see it, I had a nice shock one day when I had the bare croc clip in my hand and leaned on the chequer plate platform round the machine, the earth cable in the plug top had been left long enough to touch the live pin of the 13amp top in the days before pins were shrouded to protect small fingers so the scope was live. A pretty dodgy setup at the best of times but it works, sooner or later it will bite you though. My boots must have been good insulators as I didn't even get a tingle until I was earthed. Why is an electric shock so hilarious for everyone but the victim? although I was on the receiving end that time I still can't help laughing when it's someone else.

                                      Mike

                                      #303491
                                      SillyOldDuffer
                                      Moderator
                                        @sillyoldduffer

                                        Differential probes eh! I've been messing with oscilloscopes for 50 years and this is the first time I've heard of such a thing. I wonder what else I've missed? The older I get the more I realise I've not being paying attention. They're a bit dear though. uYAAOxyCepSa8EO”>LINK

                                        Edit strange corruption of the ebay link.  And now it's attached to my signature.  Weird.

                                        Dave

                                        Edited By SillyOldDuffer on 20/06/2017 21:58:23

                                        Edited By SillyOldDuffer on 20/06/2017 22:00:13

                                        #303494
                                        Stuart Bridger
                                        Participant
                                          @stuartbridger82290
                                          Posted by Mike Poole on 20/06/2017 21:45:50:

                                          You could let the scope float by disconnecting the earth, to indicate the earth was disconnected we used to have a long earth and pull it out of the plug top so you could see it, I had a nice shock one day when I had the bare croc clip in my hand and leaned on the chequer plate platform round the machine, the earth cable in the plug top had been left long enough to touch the live pin of the 13amp top in the days before pins were shrouded to protect small fingers so the scope was live. A pretty dodgy setup at the best of times but it works, sooner or later it will bite you though. My boots must have been good insulators as I didn't even get a tingle until I was earthed. Why is an electric shock so hilarious for everyone but the victim? although I was on the receiving end that time I still can't help laughing when it's someone else.

                                          Mike

                                          When I worked in an electronic repair shop, one of my colleagues used this trick. A certain piece of kit had a logic board where for some reason the signal ground was floating at I think about 350V DC. Highly unsafe, but apparently the only way to troubleshoot. Everyone kept well clear when he was working in this way.

                                          Edited By Stuart Bridger on 20/06/2017 22:25:56

                                          #303495
                                          Lee Goulding
                                          Participant
                                            @leegoulding74917

                                            Ok so here's my attempt at wiring into the Mesh configuration any advice if this is correct.

                                            A – Red/Brown

                                            B – Yellow/White

                                            C – Blue/Black

                                            N – No Wires Connected

                                            img_5459.jpg

                                            Edited By Lee Goulding on 20/06/2017 22:31:07

                                            #303558
                                            Les Jones 1
                                            Participant
                                              @lesjones1

                                              Hi Lee,
                                              You now have it wired correctly for 240 volt delta (Mesh) operation.

                                              Les

                                              #303565
                                              Lee Goulding
                                              Participant
                                                @leegoulding74917

                                                Hi Les

                                                Thats great thanks for confirming that..

                                                #304035
                                                Lee Goulding
                                                Participant
                                                  @leegoulding74917

                                                  Hi All

                                                  The power on/off switch on the lathe has had a 3 phase plug on the end that has been removed and I now have 4 wires which I'm not sure I need with the inverter and control pendent and if I need it connected or not but it would be good to have the power switch on the lathe working as opposed to just using the isolation switch to turn it on

                                                  The question is how would I connect that cable ?

                                                  Thanks

                                                  #304039
                                                  David Jupp
                                                  Participant
                                                    @davidjupp51506

                                                    Preferably not. In most cases any switch between VFD and motor is an invitation to blow the output stage of the VFD.

                                                    You could re-wire the switch into the control circuit, or maybe in the mains supply to the VFD.

                                                    #304042
                                                    Lee Goulding
                                                    Participant
                                                      @leegoulding74917

                                                       

                                                      Hi David

                                                      So would I use the existing 4 core wire to wire to the mains section of the VFD ?

                                                      Which wiresas there's only a L1, L2 and Earth on the live side of the VFD

                                                      Thanks

                                                      Edited By Lee Goulding on 24/06/2017 19:09:03