  • #302866
    Lee Goulding
    Participant
      @leegoulding74917

      Hi All

      I'm trying to install a Mitsubishi E500 inverter with pendant to a Boxford 280 3 phase motor and I know I need to wire the motor to Delta but what wire should I use to connect the Inverter to the motor

      Thanks

      Advert
      #31892
      Lee Goulding
      Participant
        @leegoulding74917
        #302873
        Ian Parkin
        Participant
          @ianparkin39383

          Theoretically you should use a screened cable connected at Both ends to earth or just the inverter end connected lots of discussion about that practice and which way is correct

          But I have found in practice no problem in just using 4 core flex cable…I,m now up to 19 inverter driven machines in my workshops

          #302875
          not done it yet
          Participant
            @notdoneityet

            Three core and earth of about the same rating, per core, as the incoming 230V single phase supply. No need for a screened cable if it is short lead, I believe. Details will be in the manual…. somewhere!

            If you don't know, it would perhaps be better to get the job done by an electrician.

            #302877
            Michael Gilligan
            Participant
              @michaelgilligan61133

              The supplier of my VFD recommended 'SY' cable, like this:

              **LINK**

              https://www.ebay.co.uk/itm/391433134625

              [choose an appropriate diameter to suit the current]

              … It's screened; and tough; and not expensive.

              MichaelG.

              #302879
              David Jupp
              Participant
                @davidjupp51506

                'CY' cable would be expected to be superior to 'SY' with regard to minimising radio frequency interference. CY is likely to cost a little more and won't offer quite as much mechanical protection as SY. The differences could be important in a sensitive environment.

                #302884
                Lee Goulding
                Participant
                  @leegoulding74917

                  Thanks guys for the cable advice

                  Would any of you also know if I need to add an isolation switch or breaker as it's already on and RCD from my house supply to the garage

                  Once again thanks

                  #302887
                  Martin Cargill
                  Participant
                    @martincargill50290

                     

                    When using screened cable only connect ONE end to earth. That way the screening works and does not lead to the possibility of circulating currents in the screen.

                     

                    Edited By Martin Cargill on 17/06/2017 09:09:00

                    #302889
                    Lee Goulding
                    Participant
                      @leegoulding74917

                      Ok Thanks Martin

                      #302891
                      David Jupp
                      Participant
                        @davidjupp51506

                        The 'one end of screen earthed' applies to signal cables – the ones to the pendant. It is generally recommended to earth the screen at both ends for the cable connecting VFD to motor. Best advice is to follow VFD manufacturer's guidance.

                        VFD to motor you are trying to prevent/reduce generation of RFI (conducted or radiated). Signal cables you are trying to reduce susceptibility to RFI and induced currents form elsewhere.

                        #302896
                        SillyOldDuffer
                        Moderator
                          @sillyoldduffer
                          Posted by Martin Cargill on 17/06/2017 09:08:36:

                          When using screened cable only connect ONE end to earth. That way the screening works and does not lead to the possibility of circulating currents in the screen.

                          Edited By Martin Cargill on 17/06/2017 09:09:00

                          Despite much contrary advice floating about I believe that's right. The purpose of the screen is to reduce electromagnetic radiation caused by Radio Frequency currents which are a VFD by-product. What's significant at Radio Frequency is negligible at 50Hz and in this context it's unwise to assume AC and RF are similar. In particular a loop can be an efficient radiator. Look at a TV antenna.

                          I can't find the reference but the most convincing of my books says:

                          • single shielded cables should be 'earthed' at the equipment end only
                          • the inner shield of a double shielded cable should be 'earthed' at the equipment end only BUT the outer shield should be 'earthed' at both ends.

                          I think the reason advice varies is because much depends on individual circumstances. The length of the wires, the frequencies being produced, the quality of the power earth, and the type of filter fitted all have an effect. Compounding the confusion, unless you have a wide spectrum receiver you can't tell if there's an RFI problem or not. Domestic TVs and Radios are far from ideal as test equipment.

                          Apologies for complicating Lee's question: don't over-think it! If I were Lee I'd use 1.5mm SY cable with the shield earthed at the VFD end only.

                          Dave

                          #302899
                          SillyOldDuffer
                          Moderator
                            @sillyoldduffer
                            Posted by David Jupp on 17/06/2017 09:44:05:

                            The 'one end of screen earthed' applies to signal cables –

                            Quick comment as I'm out the door in a minute, but my point is that a power cable with RF on it is best treated as a signal cable. On control wiring shielding is needed to keep muck out, on a power cable the shield is to keep muck in. In both cases a loop in the shield is more likely (at RF) to cause trouble than not.

                            Good point about following the VFD manufacturers advice though; it might be evidence based whereas I'm armchair bound.

                            Dave

                            #302900
                            Stuart Bridger
                            Participant
                              @stuartbridger82290

                              Haven't we been around this loop before???

                              #302933
                              Muzzer
                              Participant
                                @muzzer

                                (Yawn) – yes, it seems to be an old chestnut here. Some manufacturers recommend connecting both ends of a screened cable, some recommend only the VFD end. But there are lots of experts here who feel there can be only one right answer.

                                Do whatever is convenient and if you have a problem with interference (on your radio most likely), perhaps there will be an expert who can then help you to resolve it.

                                Murray

                                #302934
                                John Stevenson 1
                                Participant
                                  @johnstevenson1

                                  Yup

                                  We are not short of experts 😀

                                  #302949
                                  David Jupp
                                  Participant
                                    @davidjupp51506

                                    Mitsubishi's EMC guidelines for VFDs may be useful – **LINK**

                                    #302952
                                    Lee Goulding
                                    Participant
                                      @leegoulding74917

                                      Thanks everyone for the great replies

                                      #302953
                                      Michael Gilligan
                                      Participant
                                        @michaelgilligan61133
                                        Posted by David Jupp on 17/06/2017 15:34:33:

                                        Mitsubishi's EMC guidelines for VFDs may be useful – **LINK**

                                        .

                                        That's very impressive, David … Thanks

                                        … and I do like the fact that they offer the option to choose your own name for the download

                                        That's classy yes

                                        MichaelG.

                                        #303000
                                        Neil Wyatt
                                        Moderator
                                          @neilwyatt

                                          I'm not going to say anything…

                                          <retires hurt>

                                          Neil

                                          #303001
                                          Ian P
                                          Participant
                                            @ianp
                                            Posted by Michael Gilligan on 17/06/2017 16:12:27:

                                            Posted by David Jupp on 17/06/2017 15:34:33:

                                            Mitsubishi's EMC guidelines for VFDs may be useful – **LINK**

                                            .

                                            That's very impressive, David … Thanks

                                            … and I do like the fact that they offer the option to choose your own name for the download

                                            That's classy yes

                                            MichaelG.

                                            I beg to differ.

                                            If you pick you own name for a downloaded file the odds are that when you come to use it you will never remember its name!

                                            I used to rename downloaded data sheets etc so its name matched say, the IC it referred to because the IC manufacturers often had their own cryptic filenaming system.

                                            Nowadays I put all the PDFs in one download folder using the manufacturers/originators name. I then make shortcuts to them with sensible names.

                                            IanP

                                            #303004
                                            Michael Gilligan
                                            Participant
                                              @michaelgilligan61133

                                              Feel free to differ, Ian … I was only expressing an opinion.

                                              The website offered the rather cryptic name of < 061000.pdf >

                                              I chose < MitsubishiVFD_061000.pdf >

                                              and exported that to 'GoodReader' on the iPad

                                              MichaelG.

                                              #303005
                                              Mike Poole
                                              Participant
                                                @mikepoole82104

                                                Has anybody actually experienced any problems with interference from their VFD if they have not followed recommended guidelines?

                                                Mike

                                                #303007
                                                Michael Gilligan
                                                Participant
                                                  @michaelgilligan61133
                                                  Posted by Mike Poole on 17/06/2017 23:04:15:

                                                  Has anybody actually experienced any problems with interference from their VFD if they have not followed recommended guidelines?

                                                  .

                                                  Given that I am reliant upon my pacemaker, Mike, I decided not to risk it. surprise

                                                  MichaelG.

                                                  #303014
                                                  David Jupp
                                                  Participant
                                                    @davidjupp51506

                                                    I've looked into a case where the VFD's installed made equipment unusable – to be fair that was in a lab environment which was very sensitive to RFI (NMR measurements). There were a number of issues with that particular VFD installation.

                                                    Much of the time I suspect (as many here have suggested), most of us probably wouldn't notice any issues in a workshop setting. Might be a different story if there is sensitive equipment nearby (radiated RFI) or connected to the same mains supply (conducted RFI).

                                                    #303017
                                                    Mike Poole
                                                    Participant
                                                      @mikepoole82104
                                                      APosted by Michael Gilligan on 17/06/2017 23:39:19:

                                                      Posted by Mike Poole on 17/06/2017 23:04:15:

                                                      Has anybody actually experienced any problems with interference from their VFD if they have not followed recommended guidelines?

                                                      .

                                                      Given that I am reliant upon my pacemaker, Mike, I decided not to risk it. surprise

                                                      MichaelG.

                                                      In your situation Michael I would be very careful as well, our weld control inverters all carried a pacemaker warning and they were installed in proper cabinets and properly wired. I note that Many people just screw their VFD to the wall which does nothing to minimise any radiated signals or offer any protection from swarf ingress or coolant if used. a friend has a built in defibrillator and you wouldn't want that firing off at the wrong time.

                                                      Mike

                                                    Viewing 25 posts - 1 through 25 (of 81 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up