Re EMC filters, There is a legal requirement for them – the EMC Directive.
Steviegtr:
We are talking DOMESTIC installations not industrial the EMC requirements are very different. See link posted by Old Mart https://inverterdrive.com/group/AC-Inverter-Drives-230V/Schneider-Altivar-12-ATV12H037M2/
The fouth paragraph states (for the 1C1 VFD)
EMC Filters to EN61800-3 to the 1st Environment C1 (Domestic) for cable lengths up to 5m.
EMC Filters to EN61800-3 to the 2nd Environment C2 (Industrial) for cable lengths up to 10m.
The higher emissions for industrtral applications mean that longer cables (which act as antennas) can be used with the same filter. From your post and others you have made I believe you were mostly involved in fixed plant sytems that have even less requirements.
Apt from that, if someone else designed the panels you were buliding how do you know there were no filters? The designer may have chosen VFDs with built in filters.
There is a requirement for putting the VFD in a suitable enclosure – The Low Voltage Directive.
Again refering to the earlier link, the line beloe forth paragraph says " Cubicle mount. " VFDs are components, not finished products. The guides and manual on the linked page say " Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. " Thes units do not have the level of protection required (touch proof terminals, robust terminal covers, cable strain relief etc) to be afe if not mounted in an enclosure. ltion for full EMC compliance is 1 to two days work in a specialist facility costing around £5000 per day. No I'm not suggesting a hobby installtion should do this, but at least do the basics and use a filter.
Not interfering with one DAB radio does not mean the installtion is not causing harmfull interference elsewere. Thesting a VFD instal
You can do whatever you like in your workshop, but plese do not encorage others not to follow good advice.
Clive Brown 1.
The fact that your drive tripped the MCB means it was not suitable for the domestic installation. Disconnectin the filters is not a cure. The correct solution to this would be to run the machines off a separate supply with a less sensitive RCD. Alternatively you could use a filter with less "Y" capacitiance but this will normally be more expensive as it typically needs more or larger inductors. You also have to make sure it is effective. Just because the drive manufacturer provides a means to bypass the filter, does not mean you don't need a filter. Typically the drives with filters have passed EMC testing (in a very controlled configuration) and if the installer wishes they can use this to assume compliance in their installation (they are still responsible if it does not comply). If you do not use the supplied filter you have to assume the unit is NOT compliant and take other measures such as your own filters.
I have done this and acheived full EMC and electrical safety compliance for small machines with multiple drives. It's not always easy. Our main drive suppler brought out a new family of drives (existing ones to become obsolete). We were the first users of the new drives. When we tested a machine with the new drives fitted it failled emissions totally. This was not even a power issue were the normal filters are but on control lines that we needed. Turns out they didn't connect all the control lines when they did their compliance testing. I designed a low level signal filter tht solved it on our inital production and helped the OEM re-design the drive circuit for a proper fix. As a result we got a lifetime special discount on those drives tha added up to a lot of money over the years.
Again, I don't suggest that hobby installations need to show full compliance (legally they do but enforcment is very very low) but we should follow good enginerring practice and use these things in a safe manner. While it is extremely unlikely to happen, if there is an accident (might not be to you if it's caused by EMC) or your house burns down because of a poor installation you could end up on the wrong end of a lawsuit or denied insurance claim. It's not happened yet, lets not be the first.
Robert G8RPI