I have experienced situations where all the above has been done and still had noise problems and the only way to cure it was to disconnect the screen – just doesn’t make sense – brick wall helps.
Actually it does make sense – and it’s recommended practice! You shouldn’t confuse the safety earthing arrangements with the screening requirements – they aren’t the same thing at all. I have yet to find a situation where having a screen joined at both ends reduced any form of emissions at all – it can potentially increase them, and often it does.
With most inverters, you need a common grounding point, which is generally on the inverter itself. All the screened leads you run should have one end of the screen only connected, and generally it should be at that same earthing point that you do this. If you don’t do this, then the screen becomes a conducting path for interference, rather than the screen that it should be, and that means that it can radiate. So your earthing connections for the motor and supply should be solid, and meeting at one point, on the inverter earth tag. The screen on the incoming supply should be connected here too, and so should the screen for the motor cable and control cable, if there is one. But the other ends of these screens should not be connected to anything – they are only screens, and shouldn’t ever be used as conducting paths.
The ferrite cores you mention work effectively as a shorted-turn transformer at high frequencies, and if they get hot, then you are generating a considerable amount of interference. If you are getting radiated interference, then almost certainly this will be on the output side of your inverter, and that’s where you will get most advantage from the ferrites. The other crucial thing about reducing interference is to keep the lead lengths as short as possible – this also helps to reduce the wiring impedance – it’s impedance we are concerned about when there’s interference involved, not resistance so much.
The other problem that is frequently encountered with inverters is that they trip earth leakage systems. There is only one really effective solution to this problem, and unfortunately it’s rather expensive. That is to purchase a mains isolation transformer, and run the inverter’s input from that. But to play safe with the transformer, it’s going to have to be rated somewhat higher than the total load, and with even a 1HP motor, that means it has to be rated to supply at least 1kVA. The reasons for problems with earth leakage all relate back to what happens on the primary side of an inverter – basically your single (or even three-phase) mains supply is being converted to DC straight from the supply using socking great rectifiers – and with the best will in the world this is likely on some systems to unbalance the load. I should also point out that the whys and wherefores of this vary considerably between systems; what works fine on one mains supply won’t necessarily behave in anything like the same way on another.
And whilst you are correct about having no switching in the output, the reason isn’t quite so simple. If you look at the current output waveform from an inverter, you’ll find that it generally is a good sine wave. The voltage output isn’t though, because this is what’s being chopped by pulse width modulation to produce the current sine wave. Where switching really runs into problems though is with the reactive feedback systems that are used to sense and control the motor – switches can screw this up completely, and even leave you with dangerous situations. All the advice I’ve ever seen about this is that you can use plug and socket connections if you must – but make sure they are of good quality.