Hi Sonic,
The arrangement with the NC fault outputs on the VFD is OK. The additional relay is to cover the fact that disconnecting the input supply of a VFD does not result in a rapid stop of the motor (This was also raised by Ian P). Whenever the E-stop is pushed the Stop inputs on both VFDs must be activated. This ensures the motor stops quickly (power is provided by the “DC Link” capacitors inside the VFD and the inertia of the motor and load). The braking is DC for this so you need to set the 8.x parameters.
It is OK to use the auxillary contacts on a contactor for low voltage control circuits as they are adequately isolated. However you need two contacts, one for each VFD Stop input. So an additional relay is required or a contactor with a second auxillary contact.
There is one oddity in your circuit which could catch the unwary. The ON button is at mains potential while the OFF and E-STOP are at 24V. You would not normally expect one to be on mains. This is not good practice.
If you add an isolator switch on the supply (which you should have anyway) You can leave the 24V transformer primary permanently connected and put all of the control switches at 24V. If you are using the mains plug as an isolator then you would have to switch off at the socket.
Robert.
I don’t want to add an isolator switch on the supply and indeed that is why ON button is at mains potential. But it is safe. It is a plastic button in a plastic box. Everything is connected to a wall socket so I have a way to disconnect the circuit in a more convincing manner if needed.
About braking, I think the best is first to make some tests to see how the motors stop in different cases. Then it will be more easy to decide what to do. For example if it make sense or not to buy the braking unit.
On
17 July 2024 at 19:39 Emgee Said:
You may want to consider fitting a higher fault current RCD if at all 1 is necessary, you no doubt already have RCD protection on your workshop installation.
Even with a 30ma operating current RCD on a VFD supply tripping can be problematic, you will have 2 operating with 1 machine so makes it even more likely you will experience tripping issues.
Bond the protective braid of the SY cable to the incoming cpc (earth conductor) as advised by the VFD manufacturer, some advise connection to cpc at both ends, others only at the VFD end.
Ensure you have an adequately sized cpc conductor connected at the motor casing, even if the braid is connected both ends don’t rely on that as the resistance will be too high.
Emgee
Yes, I have a 30mA RCD for the whole house. But I want to try also a 10mA one only for the workshop. I’m aware that this old machines might have some issues with residual currents. We will see.
I start to add all components on a wood plank. It is 200x50cm and 27mm thick. Normally it is used for concrete forms. I will fix it on the wall close to the celling so nobody could reach it by mistake. And there is plenty of space left for future electrical stuff and the VFDs ventilation is perfect. There are still a lot of wires to connect.
I’m also thinking if not to make another earthing system only for the workshop. Or at least to bring a separate cable from the grounding rods. I don’t like the ground connection in the wall socket. It is a chain of cables connected together with some screwless connectors.
By chance I made also a small discovery. The 10mA RCD had a C25 marking so I assumed that is has also a 25A circuit breaker. But I noticed a tiny warning “to be protected by and circuit breaker” or something like this. So it has no overcurrent protection, it only monitors the residual current.