Star or Delta
Star or Delta
Home Forums Electronics in the Workshop Star or Delta
Viewing 23 posts - 1 through 23 (of 23 total)
  • #615366
    Barry Smith 4
      @barrysmith4
      Hi I am fortunate to have a spare 240v single phase to 240v three phase and a 240v single phase to 440v three phase in my workshop. After buying a high speed milling head I need to use one or the other to power the motor which can be wired star or delta.
      Are there any advantages or disadvantages with using 240v or 440v three phase on an induction motor (2 pole, 375W)?
      Thanks
      Barry
      Barry Smith 4
        @barrysmith4
        #615367
        David Davies 8
          @daviddavies8
          Be careful, normally motors that are dual voltage must be connected in star to run off a 415V supply and should be connected in delta to run from a 240V supply. The output power will be the same as the phase current is 1.732 times greater when connected in delta on the lower voltage (240V) supply.
          HTH Dave
          #615368
          old mart
            @oldmart
            Probably not, I thought star was for 440V and delta for 240V, no doubt the experts will enlighten us.
            #615371
            noel shelley
              @noelshelley55608
              STAR = 415v
              Delta = 240. Noel.
              #615373
              Harry Wilkes
                @harrywilkes58467
                Maybe wrong but it's my understanding 415 is the better option
                H
                #615376
                John Haine
                  @johnhaine32865
                  I'm not sure what the question is really, it's a bit garbled. But for the avoidance of doubt and for about the 10th time, as far as a 3 phase supply is concerned, if you have a 240V phase to neutral supply, the phase to phase voltage is 415V. "240v" and "415v" 3 phase are THE SAME THING. 415 = sqrt(3) x 240.
                  #615378
                  Anonymous
                    Although not explicit I assume it is implicit that all voltages are phase to phase. In theory running 415V star or 240V delta shouldn't make a difference. There might be a small advantage in using star as the lower currents might result in lower resistive losses.
                    #615386
                    Mike Poole
                      @mikepoole82104
                      Small motors are often wound for 415V star and 230V delta. When motors get large enough for star delta starting to be useful they will be wound for 415V delta and around 690V in star. A motor large enough to require star delta starting is unlikely to be encountered in the average home workshop. Always read the plate on the motor to be sure of what you have. A plate that only states 415V may not have the star point readily available and require some delicate digging to access it and rewire in delta. I am sure there will be a small motor somewhere that is wound for 415V delta which will be unsuitable for a typical single phase input VFD although single phase input with 415v output VFD units are available.
                      #615392
                      Barry Smith 4
                        @barrysmith4
                        For clarity I have 240V single phase in my workshop and have two options for running a 2 pole 375W motor.
                        The motor is capable of either running 415V star or 240V delta
                        (1) I have a spare 240V single phase to 240V VFD, and
                        (2) I have a spare 240V single phase to 415V VFD
                        My question was which of the two options (1 and 2 above) is optimal? From what has been said here and on the web there is little difference.
                        Thanks for replying
                        Barry
                        #615394
                        Nealeb
                          @nealeb
                          Barry – I suspect that you already understand the star/delta 415/240 issue. My feeling (without specific evidence!) is that if you have "real" 3-phase supply then the star/415 connection would be better as currents are lower so slightly lower cable loss – but this is unlikely to be of any real significance for such a small motor. However, a 240V in/out VFD will use the incoming supply directly via a rectifier/capacitor arrangement where the 240/415 in/out VFD will need an extra voltage step-up stage. Therefore I would expect the overall system efficiency to be slightly less in this case. But this is all a bit theoretical and the differences will be barely measurable.
                          So, the "engineering" thinking – in this case, use the 240 in/out VFD with the motor delta-connected. This leaves the other VFD free for the day you have a motor without the delta option!
                          #615400
                          noel shelley
                            @noelshelley55608
                            Nealeb has answered the question very well – and my thoughts exactly ! Noel.
                            #615409
                            not done it yet
                              @notdoneityet
                              Using some (any) conversion from single to three phase will involve some energy loss. That is for certain, definite and unavoidable. Therefore direct from the mains is always cheaper to run.
                              If a VFD, there will be some reduction in the sine wave purity. Unavoidable, however minimal.
                              VFDs always produce some energy losses in the form of mains/radio interference. These can be minimised, of course, with suitable filters.
                              A VFD may need a different circuit breaker, due to unbalanced input/output currents or other losses.
                              Overall simpler, if the three phase mains is available and already being paid for, to utilise that supply with the motor in star connection (if that is appropriate for that motor).
                              Edited to add:  The VFD option, if that is what it is, would likely afford a deal of programming – such as variable speed, soft start, etc
                              Edited By not done it yet on 29/09/2022 10:11:31
                              #615410
                              Bazyle
                                @bazyle
                                A 240 to 415 VFD is much more expensive than a 240 to 240 one. I suggest saving the 240 to 415 one for when you get a piece of equipment that has a star only motor. Even if you have raw 415 available there will be some time when the speed control on that extra machine is desirable.
                                #615416
                                  My understanding is star is better than delta for load-balancing reasons when many motors are starting, stopping and drawing current more or less randomly. Most likely in a factory or perhaps a largish workshop with several employees. High voltage also reduces resistive losses in the distribution wiring and there's lots of that in a factory, which becomes important if greedy equipment other than motors are connected – big ovens, welders, etc.
                                  For small scale use the advantage lies with delta motors, but I doubt the difference is detectable in a small workshop. If I had both high and low voltage 3-phase I wouldn't bother changing motors from star or delta, I'd just plug them in to the appropriate supply.
                                  Industrial best practice is worth knowing about but it's not always useful in a home workshop. There's an enormous difference between a hobbyist using a few simple machines in his shed and large-scale manufacturing! The latter has to optimise almost everything, and are likely to take professional advice from electrical engineers and others when configuring production: in that scenario a few percent shaved off the electricity bill is big money. Home workshops are much less fussy – we tend to do low intensity general-purpose work, when it suits us, and don't work against the clock to make a profit. It's not worth chasing micro-efficiencies, unless of course, it's done for interest or learning!
                                  Robert Atkinson 2
                                    @robertatkinson2
                                    You don't mention the sizes of the VFDs. The motor is small at 375W so use the smaller of the two VFDs. If both the same do as Bazyle says and use the 240 output one and save the 415V for when you don't have the option.
                                    Robert G8RPI.
                                    #615444
                                    John Haine
                                      @johnhaine32865
                                      Posted by SillyOldDuffer on 29/09/2022 10:38:37:
                                      What are these high and low voltage supplies If you mean 415 or 240 then they are the same supply!!! It just depends on how you measure them.
                                      #615447
                                      not done it yet
                                        @notdoneityet
                                        Posted by Robert Atkinson 2 on 29/09/2022 12:44:54:
                                        Robert G8RPI.
                                        I would suspect the 240>415V is a converter, not a VFD. A converter will be either static or rotary. Running a rotary converter obviously means running another motor, for a start. On top of that, I believe the rotary converter requires ‘changing over’ every time a motor may need to be reversed (it seems that that of doubleboost is like that?).
                                        Static converters are a compromise on motor size, so must only be most efficient for one power output?
                                        Personally, I would be changing any motor from star to delta and running a 240V output VFD in most circumstances – unless I had a 415V grid supply.
                                        Edited By not done it yet on 29/09/2022 13:44:37
                                        #615462
                                        Jelly
                                          @jelly
                                          Posted by John Haine on 29/09/2022 13:23:07:
                                          I mean, you do see both 240v per phase (commonly called 415V) and 400V per phase (commonly called 690V) three phase supplies in fairly common use…
                                          I always felt that the line to line voltage of the "normal" three phase being similar sounding to the phase voltage of the the "added beans" supply, added an unfortunate element of confusion which wasn't really helpful and meant you had to be just a bit more specific in your language when talking about installations with both systems in them…
                                          In any case I doubt OP would have a supply like that mind, and even if they did it would still be "Low Voltage" (i.e. 50V < P.D. < 1000V) just a non-standard one.
                                          #615470
                                          Jelly
                                            @jelly
                                            Posted by not done it yet on 29/09/2022 13:41:32:
                                            Robert G8RPI.
                                            That's down to his particular setup, rather than RPC's in general; if you watch any of Keith Rucker's videos you'll see him frequently reversing motors on a three phase supply that comes from an RPC.
                                            A well made RPC, using a modern motor, with the phases balanced and tuned to the desired range of load outputs, should be highly efficient too, with about 95% efficiency at the power rating they're tuned for, and up to about 90% across the full range of possible power outputs (smaller RPC's will see a drop in efficiency, commensurate with the drops in efficiency smaller electric motors have).
                                            The off-load power consumption of a RPC is directly related to how good a motor was used as the autotransformer, I know the old rule of thumb is for the no-load power consumption being 30-40% of full load, but with modern IE2 & IE3 motors the reality should actually be much lower… Like 15% (for a 0.75kW load) going down to 6% (for a load >30kW).
                                            Which fits my experience the 11kW motor in my RPC consumes about 8-9% of full-load at no-load (which is actually slightly better than the manufacturer's databook value), combined with the power factor of 0.88, and the new price cap price of £0.52/kWh that means it would cost me about £0.40 for each hour it's left idling…
                                            That's not nothing, but it's also sufficiently small that it would need to run on idle for several thousand hours before it cost me as much as buying 7 VFD's for all the 3-phase motors in the workshop, and I have the option to turn it off when it's not actively in use.
                                            #615475
                                            Robert Atkinson 2
                                              @robertatkinson2
                                              Robert G8RPI.
                                              The OP clearly states in his second post that he has two VFDs
                                              #615476
                                              Robert Atkinson 2
                                                @robertatkinson2
                                                Posted by Jelly on 29/09/2022 16:10:14:
                                                A VFD output voltage is always quoted PHASE to PHASE. This is because there is no neutral on the output.
                                                Modern VFDs rectify the input voltage to DC and then use solid state switches (MOSFETs or IGBTs) to "chop it up at high frequency into pulses. The timing and width of the pulses are filtered (often just by the motor inductance) into low frequency sinewave outputs. The DC voltage needs to be similar to the peak output voltage. This is easy for 240V in and 240V out, you just rectify and smooth the input. For 240V in 415V out you have to boost the voltage. This can be done as part of the rectification (and power factor correction) circuit or high frequency franspormers on the pulses. Either way it adds components and cost.
                                                Robert G8RPI.
                                                #616139
                                                Barry Smith 4
                                                  @barrysmith4
                                                  Hi many thanks for your detailed replies, I have gone down the route of using the 240v to 415v VFD/Inverter and running the motor as star. Interestingly the 215 to 415 inverter was of UK Amazon for £70 and is rated at 3HP. I notice the same model has gone up a lot, but for £70 I was prepared for it to break knowing that Amazon would step in and offer a refund.
                                                  That said its been working OK on the main 415v two speed motor that runs the std machine (an Aciera F3) on and off for the past two years. The only thing I typically changed in the programme setup is to increase the slow start and decrease the stop speed as this save blowing fuses and of course wired the remote up for control.
                                                  Cheers
                                                  Barry