  • #114247
    Anonymous
      Posted by jason udall on 12/03/2013 09:28:45:

      BTW

      REACTANCE IS ……IMAGINARY

      Only in the sense that it includes the factor 'j'. It may lead to complex impedance, but still results in real currents flowing in the real world.

      Andrew

      Advert
      #114249
      Sub Mandrel
      Participant
        @submandrel
        Posted by jason udall on 12/03/2013 09:28:45:

        BTW

        REACTANCE IS ……IMAGINARY

        RESITANCE IS FUTILE!!!

        #114254
        Cornish Jack
        Participant
          @cornishjack

          … and all of the foregoing explains why, when teaching aircraft electrics to flight crew, if anyone mentioned reactive loads, the response was short, sharp and (as long as no ladies present) quite rude!! Life is too short!

          Rgds

          Bill

          #114268
          jason udall
          Participant
            @jasonudall57142
            Posted by Stub Mandrel on 12/03/2013 10:30:13:

            Posted by jason udall on 12/03/2013 09:28:45:

            BTW

             

            REACTANCE IS ……IMAGINARY

            RESITANCE IS FUTILE!!!

            But IMPEDANCE IS COMPLEX..

            ( yes Andrew)

            BTW as an engineer I want a jphone

             

            Edited By jason udall on 12/03/2013 13:11:33

            #114285
            john swift 1
            Participant
              @johnswift1
              Posted by jason udall on 12/03/2013 09:28:45:

              BTW

               

              REACTANCE IS ……IMAGINARY

              takes me back to the 1970's and complex numbers !

              **LINK**

               

              the forced adoption of a green world wide switch mode power supplies ,very often without a real on /off switch , has compromised safety

              from exempting ATX computer power supplies from PAT testing to the use of leaky non earthed switch mode supplies used for digital TV's and satellite receivers laptops , external hard drives , modems etc

              very often the insulation barrier between the live part of the psu circuit and what you expect to be the isolated DC output , is bridged by a capacitor and in some designs a 1M resistor

              ( see C27 on page 2 of the laptop psu design )

              European Union has decided that the suppression of RF interference is more important than safety

              with a single 25W power supply the leakage current should be "safe" , even though your voltmeter may show 80V AC or more , between the "isolated" DC output and earth

              the inexpensive supplies made to a price are likely to be of questionable quality and more of a safety risk

              when you have several non earthed pieces of equipment connected together

              don't be surprised if the total leakage currents are enough to give you a shock (no prize for guessing how I know )

              the now banned non green double insulated adaptors are likely to measure about 6V AC

               

              laptop PSU design        http://www.onsemi.com/pub_link/Collateral/AND8397-D.PDF

              ATX PSU design           http://www.onsemi.com/pub_link/Collateral/TND359-D.PDF

               

              without power factor correction , the high pulsed current distorts the mains supply , flattening the top of what should be an AC sinusoidal waveform

              this adds to the cost of ensuring supply is within specification

              which adds to our utility bills !

               

               

                   John

              Edited By john swift 1 on 12/03/2013 16:44:42

              #114288
              Russell Eberhardt
              Participant
                @russelleberhardt48058
                Posted by Andrew Johnston on 12/03/2013 09:53:36:

                Posted by jason udall on 12/03/2013 09:28:45:

                BTW

                REACTANCE IS ……IMAGINARY

                Only in the sense that it includes the factor 'j'. It may lead to complex impedance, but still results in real currents flowing in the real world.

                Andrew

                Ah! A real engineer. Everyone else calls it "i".

                Russell

                #114291
                Billy Mills
                Participant
                  @billymills

                  Swarf,

                  The choke input filter is very widely used at high frequencies inside many SMPSU's and several times over on motherboards, it can be just half a dozen turns of wire on a ferrite core. At 240 V 50Hz however it is a bulky expensive part which has a larger than normal core because of the very strong direct current requirement. The peak current without a choke can be very high, if you want to draw 10A DC then the peak current goes towards hundreds of amps for a mS or so. Active PF correction uses an inductor at a much higher frequency so it is small and cheap, as Andrew has indicated you can solve the "chunk out of the mains" issue that happens when you have full wave capacitor input supplies.

                  This is also a reason why old style PF measurements can be very misleading because they often assume sinusoidial current and voltage instead of a massive current spike. The impulse does not help the Supply Companies or the Consumer, the current demand can cause the rectified voltage to be much lower than expected- certainly so on a long extension lead.

                   

                  Jason's comments about IT testing are off track. In the US they have 110V line and neutral just as we have 240V line and neutral. Because many US outlets are unpolarised and do not have a third earth connection you cannot say which conductor is line and neutral so the inlet cap is between the two wires. Plastic insulated SMPSU's can have two wire connections with one inlet filter or three pin inlets with a delta filter using a third earth return ( sometimes called FG). There is no path between the input filter and 0V on the two wire types that I have seen.

                  All ATX supplies that I have inspected have delta filters and require an earth connection otherwise the metalwork floats up to half line due to the capacitor tap. The PAT inspection requirements for IT equipment are different because -in particular- the earth continuity high current test would cause extensive damage to the equipment. This is a legit outcome because only the PSU is a risk item, if you applied the test from power cord to any exposed metalwork you could burn out tracks on the motherboard and any other boards. It is certainly the case that many -if not most- PC's are badly made, leave out EMC filtering parts and put people at risk. That is how you can get an ATX PSU for £7.00 trade in the UK.

                  Billy.

                   

                  Edited By Billy Mills on 12/03/2013 17:48:37

                  #114307
                  Ken Fox
                  Participant
                    @kenfox67095

                    We need some consistency in nomeclature here. Consider a 3 phase power supply because most of us are familiar with such things. You can get three voltages from it, A-B, B-C and C-A which are 120 degrees apart and/or for a 4 wire 3 phase system you can get A-N, B-N and C-N, again 120 degrees apart but the voltage amplitudes are different. You can connect a 3 phase motor to A,B,C wires and get a rotating field in the motor which will make it spin. You can take any 2 wires, which some here are calling phases but you will only get single phase power from them and they will only work on a single phase motor which only works because of mechanical and mathematical trickery. so keep in your minds the diffence between "wire" and "phase'.

                    Merry— I, in turn am not sure what you mean in 2. I think we are saying much the same thing here.

                    When I mentioned 2 phase in point 3, I was referring to 2 sinusoidal voltages 90 degrees apart which was used many many years ago. This system can generate a rotating field inside the motor and works perfectly well. It fell out of favour because it takes a bit more copper per HP in the powerlines. In fact with a bit of mathematics you can prove that 3 phase gives the minimum copper per HP of any of them. Actually the difference is not much. To come back to your point, two phases 180 degrees apart is single phase cannot generate a rotating field.

                    You are quite right, the distortion is high and this brings its own consequences in terms of what voltage a rectifier will deliver for a given AC voltage. The IEEE definition of pf is W/V*I where W is watts, V is volts and I is amps, all measured by electrodynamomer instruments; sort of old technology but there it is.

                    My understanding of a "rotary phase converter" is a system in which you feed a 3 phase motor with single phase on any 2 of the 3 power supply wires then get 3 phase from the 3 motor terminals. Sort of a buck-she arrangement but it's better than nothing if thats all you have. "M-G set" is a more general term in which you use a separate motor to drive a generator. This term is used for any such arrangement be it 1 ph AC to 3 ph AC, 1 or 3 phase AC to DC or DC to AC, any number of phases.

                    As I said, it is all in the nomenclature.

                    Ken

                    #114311
                    Swarf, Mostly!
                    Participant
                      @swarfmostly

                      Hi there, all,

                      I still haven't located my copy of the TI application note – watch this space.

                      Billy, thank you for your post. The fact that, in a full-wave choke input filter system, the current flows for the whole half-cycle in each diode (rather than the extremely high but narrow current spike with a capacitor input filter ) is the unsung merit of the choke input filter. I did mention this in my initial post but perhaps I didn't talk it up as much as it deserves.

                      The choke inductance has to be greater than some critical value for the particular value of the load resistance. This varies as the load current varies, leading to the use of a 'swinging choke' in which a gapped core is used to control the saturation of the core and hence the inductance. I guess designing these is a dying art.

                      Sort of following on from Ken's post, I seem to remember from my college electro-technology lectures (some fifty-eight years ago) that in a three phase alternator, the lap and lead of the stator windings can be chosen so that harmonics are cancelled, improving the purity of the alternator output waveform. The harmonics arise because the rotor flux spacial distribution only approximates to a sinusoidal shape. Any more than that is lost in the mists of time and my aged neurons!

                      Best regards,

                      Swarf, Mostly!

                       

                      Edited By Swarf, Mostly! on 12/03/2013 21:45:06

                      #114326
                      Russell Eberhardt
                      Participant
                        @russelleberhardt48058

                        There's a comrehensive explanation of electronic PFC here for anyone interested.

                        Russell.

                        #114356
                        Ken Fox
                        Participant
                          @kenfox67095

                          Russell

                          Thanks for that reference. There is a lot of good stuff in it and it goes into my favorites

                          Ken

                          #114359
                          Ken Fox
                          Participant
                            @kenfox67095

                            Swarf Mostly

                            My education in electrical engineering is the same vintage as yours.

                            In a rotating AC generator the major contributers to non-sinusoidal waveform, as I remember it are slot ripple which is high frequency and non sinusoidal flux distribution in the air gap which can give either a flat topped or peaked wave shape. Various games were/are played to reduce these effects such as slot skewing, shaping of the pole face and, I presume your lap and lead of stator windings although I'm not familiar with these names.

                            At one time I owned a small cheap and dirty AC generator which had a very large slot ripple and also an almost flat topped wave shape. About all I can say for it is that it would run a light bulb or small hand tool. I have a better one now which uses inverter technology and I'm very impressed by its wave shape. You cannot see any non sinusoidal component in it though it's probably not perfect.

                            In a large utility with many generators in parallel things like slot ripple tend to cancel out as the various machines have different ripples.

                            Ken

                            #114369
                            Russell Eberhardt
                            Participant
                              @russelleberhardt48058

                              Posted by Ken Fox on 13/03/2013 14:49:29:

                              My education in electrical engineering is the same vintage as yours.

                              … and mine. This is where I learned about electrical machines. HSE would have a field day!

                              Russell.

                              Edited By Russell Eberhardt on 13/03/2013 16:06:10

                              #114438
                              Anonymous
                                Posted by MICHAEL WILLIAMS on 09/03/2013 10:44:59:

                                (1) Some plonker in a shed with a dodgy DIY converter is is not likely to affect the supply system itself very much – but that is not and hasn't been the point . That plonker is individually himself breaking the rules and is liable to be investigated and either shut down or made to install satisfactory equipment .

                                Michael: I'm unable to find any specfic rules applying to domestic electricity consumers regarding the use of converters; can you elaborate?

                                Andrew

                                #114530
                                Muzzer
                                Participant
                                  @muzzer

                                  Billy – "The peak current without a choke can be very high, if you want to draw 10A DC then the peak current goes towards hundreds of amps for a mS or so." That's an old chestnut (myth). The theory is actually very simple and the worst case current (even with a hard supply and ideal components) is actually part of a (modest) cosine waveform, not a peak of indeterminate amplitude. I know, having spent many years in this field.

                                  "It is certainly the case that many -if not most- PC's are badly made, leave out EMC filtering parts and put people at risk. That is how you can get an ATX PSU for £7.00 trade in the UK." It's illegal to sell PSUs (or any other potentially hazardous electrical equipment) in the EU that doesn't meet a whole raft of EMC and safety standards. If it's got a CE (or UL or CSA) mark, then you can be fairly certain it's significantly compliant. If you find that someone's selling such a component with the marking on but that you think isn't compliant, you should contact trading stds etc.

                                  Nothing personal but we need to get a few things straight!

                                  Interestingly, "passive PFCs" are simply large inductors on the input of passive diode rectified capacitive filter PSUs that smooth out the input current so that it's much closer to a sine wave. Of course, it doesn't actually lead to a very good power factor but it's cheaper than an active PFC for small (<300W) loads. The filter sections at the front of PSUs are actually aimed at preventing the switching voltage (noise) being conducted back into the mains and generally have very little effect on the current waveform. The legislated limits for conducted noise are of the order of millivolts and cover all frequencies up to 30MHz.

                                  Merry

                                  #114537
                                  MICHAEL WILLIAMS
                                  Participant
                                    @michaelwilliams41215

                                    (1) Re : Electrical equipment .

                                    **LINK**

                                    All supply companies have a similar guidance document .

                                    (2) Re : Smoothing circuits for rectified AC .

                                    When designing smoothing circuits it is sometimes nescessary to consider transient response to rapidly varying loads . An example of this type of load is one which is doing a lot of ON OFF switching all the time – like a chopper drive to a motor .

                                    Michael Williams .

                                     

                                     

                                    Edited By MICHAEL WILLIAMS on 16/03/2013 10:09:03

                                    #114700
                                    Muzzer
                                    Participant
                                      @muzzer

                                       

                                      (1) Re : Electrical equipment .

                                      **LINK**

                                      All supply companies have a similar guidance document .

                                      This is for industrial users requesting the utility company make a new connection for their facility. I think generally speaking, there will be very few plonkers in sheds that find their existing connection inadequate.

                                      Meanwhile, the regulations governing the development and sale of electrical equipment address these concerns, so said plonkers will struggle to find equipment that cause those kinds of issues in the first place. Unless said sheds contain some very impressive experimental electrical equipment!

                                      Those regulations cover the issues in the link (flicker, harmonics, EMC etc), as well as the concern in (2). You can start with EN61000 but there are quite a few others to be met as well. And that's before you even start on safety certification….. **LINK**

                                      Merry

                                       

                                      Edited By Murray Edington on 18/03/2013 18:36:53

                                      #114705
                                      MICHAEL WILLIAMS
                                      Participant
                                        @michaelwilliams41215

                                        I've added you to my long list of great experts .

                                        #114720
                                        Anonymous

                                          Michael: Thanks for the link to the electricity supply guidance document. I'm pleased to say that in general I meet the requirements, as the biggest three phase motor I run DOL is 5hp. My TIG welder also comes in under the single phase limits. However, the less said about the air compressor the better.

                                          Reading between the lines I assume that the document is aimed primarily at commercial users? I doubt many domestic users would understand the terms used, know how to measure the parameters mentioned or have the equipment for the measurements.

                                          Regards,

                                          Andrew

                                          #114740
                                          MICHAEL WILLIAMS
                                          Participant
                                            @michaelwilliams41215

                                            Hi Andrew ,

                                            Reading between the lines I assume that the document is aimed primarily at commercial users?

                                            Whilst the bulk of problem situations investigated are industrial the supplier will investigate any observed difficulty or react to any complaint from domestic users in exactly the same way .

                                            Most suppliers have an investigating and advisory team permanantly available but a few contract out domestic problem solving to electrical firms .

                                            General policy with domestic users is to advise and correct rather than invoke any legal process .

                                            Most commonly investigated domestic user problems arise from welders run at high power from cooker sockets .

                                            I doubt many domestic users would understand the terms used, know how to measure the parameters mentioned or have the equipment for the measurements.

                                            Generally domestic users are assumed to have bought equipment which is approved for domestic use and connected up to a modern electrical installation which is also approved . Equipment producers and electricians should normally do all nescessary tests and checks .

                                            Apart from welders problems on domestic premises usually arise from DIY installations and old and home made equipment and from old wiring systems with primitive earthing .

                                            Some of the low power interference problems which affect TV and computers are reduced greatly just by installing full modern specification earth wiring .

                                            Unsatisfactory electrical installations and use of inappropriate electrical equipment on domestic premises can sometimes be investigated by your local authority and can invalidate insurance cover .

                                            Above information as obtained from a contact in the industry – not much of it seems to be officially written down anywhere .

                                            Regards ,

                                            Michael Williams .

                                          Viewing 20 posts - 51 through 70 (of 70 total)
                                          • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                          Advert

                                          Latest Replies

                                          Home Forums Beginners questions Topics

                                          Viewing 25 topics - 1 through 25 (of 25 total)
                                          Viewing 25 topics - 1 through 25 (of 25 total)

                                          View full reply list.

                                          Advert

                                          Newsletter Sign-up