Problem with an Altivar 11 driving a 3 phase motor.
Home Forums Workshop Tools and Tooling Problem with an Altivar 11 driving a 3 phase motor.
  • #537292
    Andrew Tinsley
      @andrewtinsley63637
      I use this VFD to check out 3 phase motors after converting from star to delta. Last time I used it, it was fine. This afternoon I connected up a motor and switched on, the usual rDy (ready signal) was displayed. Flicked the forward run switch and nothing except the display showing zero Hertz, same with reverse switch. Checked out the motor on a second Altivar and it ran perfectly. So it seems the little old Altivar 11 has a problem.
      I checked out every parameter in the program (against my list of value) nothing had changed. Checked that the common output voltage for digital inputs were present. Yes +15 Volts was present and the mechanical switches worked as they should.
      Now these all singing and dancing VFDs are usually fast enough to tell you what the fault condition is (usually motor fault) but often VFD problems as well. But not this time!
      Not sure where to check next, but it seems that the switch digital inputs pull the +15 Volt common supply to zero if it is connected to an analogue input. Now this can't be correct?
      Andrew.
      Andrew Tinsley
        @andrewtinsley63637
        #537329
        old mart
          @oldmart
          Check your switches if they are remote.
          #537341
          Andrew Tinsley
            @andrewtinsley63637
            Hello Old Mart,
            I did say in the original post that the switches were checked and found to be working correctly.
            Andrew.
            #537490
            old mart
              @oldmart
              Sorry, I had a little trouble with the cheap switching which I used with the Altivar 12. A spray with AC90 did the trick, Servisol switch cleaning lubricant would have been better. I tried googling Altivar 11 and there was a lot of info, including the factory reset.
              Edited By old mart on 01/04/2021 15:36:28
              #537493
              Andrew Tinsley
                @andrewtinsley63637
                Thanks for that, I have the manual for the Altivar 11 and that isn't helping for this problem! I suppose I can't complain as I purchased it second hand for very little money. It has been first class in sorting out various problems with old motors which come through my shop, so it doesn't owe me anything.
                I still have a sneaking suspicion that it is something simple that I am missing, so it won't get binned yet.
                Thanks again,
                Andrew.
                #537510
                LADmachining
                  @ladmachining
                  Is the inverter just ramping the test motor up to full speed (100%) on pressing start, or do you have a potentiometer to vary the speed?
                  Anthony
                  #537528
                  Andrew Tinsley
                    @andrewtinsley63637
                    Hello Anthony, the inverter is ramping up to 50 Hz over 5 seconds (or should be!) no poteniometer control, just another thing to give trouble!
                    Andrew.
                    #537541
                    Simon Williams 3
                      @simonwilliams3
                      Apologies to the OP for butting in, but :
                      Old Mart, could you possibly point me at the reference you found for a factory reset?
                      I have two of these units (Altivar 11) I bought from Germany, but they have been programmed and locked with remote software and I have failed to connect to them, let alone guess the password. I'd love to try a factory reset. Both of them work OK but not at the settings I want to use.
                      Many thanks in anticipation and excitement (it doesn't take much these days!)
                      Best rgds to everyone, hope your Easter Egg chocolate weekend goes well.
                      Simon
                      #537548
                      old mart
                        @oldmart
                        I googled Altivar 11 and there were lots of hits including how to do factory resets. I don't know what the difference between the model 11 and the 12. I bought a 12 model from the inverter drive supermarket because they have produced their own quick start guides which even somebody like me can understand. All of the external wiring, speed control and switchgear is shown clearly, as well as the programming of the most useful parameters. The original manuals are also available for the electricians amongst us.
                        #537654
                        Andrew Tinsley
                          @andrewtinsley63637
                          Hello again,
                          I have found the fault, there is no bus voltage, so hardly surprising it doesn't run! The diode block is sealed and probably contains the output devices as well. Probably zero chance of a spare block, unless anyone else knows different?
                          The usual suspect for zero bus volts is the precharging resistor. It reads 46 ohms and is labelled up at 47 ohms, so it looks like a one way trip to the tip.
                          Andrew.
                          P.S. Even if the parameters are pass word protected you can do a factory reset. I have done it once from a site on the net. You should find it with a bit of googling.
                          #537655
                          old mart
                            @oldmart
                            Good result, are the 11 series made in France? The 12 series one that I bought is made in Indonesia.
                            #537675
                            Andrew Tinsley
                              @andrewtinsley63637
                              Hello Old Mart,
                              I really don't know, There is no mention of country of manufacture on the unit!
                              I cannot see any of the 3 output devices anywhere on the PCB and hence assume they are in the block with the Bus diodes. The block has quite a few holes in it and very long pins on the underside of the pcb which fit through said holes; Thee of the 15 or so pins have ferrite beads on them, so I assume they are from the 3 output devices.
                              Very annoying having to scrap the VFD for want of a bridge rectifier, I can't even squeeze one in on the heatsink, even if I worked out the pin out!
                              Thanks for your interest,
                              Andrew.
                              #537838
                              old mart
                                @oldmart
                                Can you get a photo of the rectifier, there are some very knowledgable people on this forum who might have a solution.
                                #537842
                                Andrew Tinsley
                                  @andrewtinsley63637
                                  Hello Old Mart,
                                  I will disassemble it again and this time I will cut open the sealed block and see what there is inside. As the Altivar 11 is quite an old design, it may be that the full wave rectifier is a simple diode set up. I believe more modern designs use SCRs and are used to tame the surge current on switch on rather than a surge resistor and shorting relay.
                                  Assuming they are diodes, then I just may be able to do a repair.
                                  Andrew.
                                  #537873
                                  old mart
                                    @oldmart
                                    You have very little to loose, but don't bin it if you have more than one of the same model. I thought I had found a wiring diagram on line, but was reluctant to sign up for whatever just to look at something which might not be for that model after all.
                                    #538666
                                    Andrew Tinsley
                                      @andrewtinsley63637
                                      I eventually got around to dismantling the Altivar 11 and cut open the sealed block. Unfortunately there is no chance of repairing it.
                                      I took the part number from the block and did a search for it. I found a Chinese company selling new ones for £15 and £4 postage. So one is now on order. The last item I had from China took a couple of weeks to arrive, so hopefully I should have a working VFD by that time.
                                      I will report back with the results,
                                      Andrew.
                                      #538668
                                      old mart
                                        @oldmart
                                        Fingers crossed, then.
                                        #540732
                                        Andrew Tinsley
                                          @andrewtinsley63637
                                          Well the new rectifier / output block arrived this morning,. The leadouts were soldered in, unlike the original where the leads were a push fit.into the block.
                                          With some considerable difficulty, I managed to install it . After putting the Altivar back together, I was rewarded with a working VFD, so worth all the aggro.
                                          Andrew.
                                          #540733
                                          Andrew Tinsley
                                            @andrewtinsley63637
                                            Really must refrain from double clicking the post button!
                                            Edited By Andrew Tinsley on 20/04/2021 18:38:09