Presumably its a rotary phase converter with a step-up transformer to give 440 volts and the contractor coils are correctly connected across the transformer outlets.
If so its under-rated for the job. Those two speed motors are notorious current hogs on start-up and if the transformer cannot supply the full current needs the voltage drops enough to let the contractors pull out. As soon as the contractors pull out full voltage is restored so they pull back in. Effect on motor is sort of like getting a dead car rolling by rocking it back and forth. After three or for chatters (rocks) the thing gets moving on the the current the transformer can supply.
Electrically savvy folk with appropriate knowledge, experience, understanding and instrumentation can sort such problems. Usually doesn't take a lot to go from almost works properly to does work properly, albeit with perhaps less safety margin than you'd ideally want. If you know what you are doing.
For ordinary guy in the shop best solution is brute force with a bigger converter. On home built converters enlarging the rotary element / pilot motor can fix the problem. Were I to do a home brew (which I never shall again) I'd probably use a 7.5 HP pilot and a theoretically oversize transformer.
Commercial manufacturers have to hit a sensible price / performance ratio so sometimes a device that works perfectly well for all normal use will fail for the edge cases.
If its a static converter basically fergedditt. Generally running such motors is beyond their pay grade.
Clive.
.