OK we anre now deviating away from the original issue of LEAKAGE currents of around 0.03 amps (30 milliamps mA) into Mains earthing systems that have to carry FAULT currents of hundreads of amps. The leakage currents form VFDs and similar devices are not due to faults. A resistance of 10,000 Ohms (10k) with 240V (UK mains) across it will cause a current of 0.024A to flow (Ohms law I = V/R). This close to the 30mA trip current of a domestic RCD. !0K is thousands of times higher resistance than a mains earth. Lets forget about earthing systems.
SOD. The Fluke picture is not helpful becuase it is addressing using a clamp meter for it's typical application of mesuring load current not leakage. I can design a vey simple means of detecting leakage current. A current transformer with two primary windings one carrying the current in the line the other tha current in the neutral. Oh wait that's a current clamp meter around live and neutral. It's also what is built into most electrical installation meters.
Chris P. I said a junction box screwed to wood and exposed to water (a fault condition) not a new, dry box.
The earthing system in use TT, TNC-S etc is irrelevent to this discussion.
As for finding where the leakage is that is not difficult given a sensitive clamp ammeter. First measure and note the leakage current by placing the live and neutral in the jaws of the clamp meter.
To deterine if the leakage is through the desigined "earth" protective conductor add the earth conductor to the L&N in the jaws. Any remaining current is leakage to a connection outside the designed earth system such as damaged insulation.
This process can be carried out at an individual piece of equipment, a particular section of an installation e.g. a ring and the whole installation. Thia allows the exact source of the leakage to be identified. However the fact you would be dealing with individual conductors means that the first layer of protection against shock e.g. equipment case, outer insulation has been removed exposing you to a higher risck of electric shock. This work should only be carried out by competent persons.
As an extension to the testing, it is also possible to tell how much of the leakage current is due to the filters in a VFD or similar. To do this you need a phase sensitive current sensor. As the filter leakage is due to capacitors the current is ninety degrees out of phase with that caused by "normal" resistive leakage.
Note that this intentional current nomally flows through the metal case of the filter as well as any earth wire. You should never earth a filter or VFD purely by bolting it to an earthed metal panel ther must also be a flexible cable connection. This is because if the filter or VFD was unbolted from the panel the leakage current would become a shock risk to anyone touching it.
I've designed this sort of equipment. An example is protection of the high current feeder between a generator and a circuit breaker panel without using fuses in the feeders. You just run the feeder conductor through a current transformer at the generator end and another at the load end. Connect the transformers secondaries in series anti-phase to a sensitive current relay. Load current flows through both transformers and cancel out. Any current due to a fault between the two transformers (to neutral or "earth" only flows through the generator transformer and is not cancelled causing the sensitive relay to operate and shut down the generator.
Robert.