Posted by Robert Atkinson 2 on 12/07/2023 14:51:25:
That is not correct for a VFD. There are number of issues. Firstly the VFD does not have a HF converter transformer and does not use balanced positive and negative buses. They just rectify the incoming AC to a single DC bus The topology relies on an isolated load.
Additionally the arrangement you describe will only work for a balanced load. Any inbalance between phases will affect the voltages so the "neutral" will not be at 0V with respect to all phases.
To provide a star output without a transformer requires active control of the star point (neutral) voltage. This requires it's own power driver effectively adding a fourth phase driver and additional control complexity.
Robert.
I assure you that it can and does work. Cheap VFDs won'd have the capability, but ones from the likes of Danfoss manage it. For that matter, if you've got an inverter TIG welder, it will be arranged that way as well. Unbalanced loads aren't a problem for any inverter, since the three generated phases are independent of each other, apart from timing. Some will fault if the unbalanced load limits are set too tight, but their purpose is to detect loss of phase in the load, not to protect the VFD.
I don't, personally, have those problems in the shed, since I use a seperate delta-star transformer downstream of the VFD/inverter in order to allow for a grounded neutral.
Regards
Mark
PS:- sorry for the thread drift everyone.