Posted by duncan webster on 01/07/2016 13:50:06:
Posted by SillyOldDuffer on 01/07/2016 13:04:15:
Posted by duncan webster on 01/07/2016 12:42:49:
Hi Duncan,
…
I wonder if you might need in-line fuses on both plus and minus? Depends on your stepper motor supply, which could be floating, or negative ground, or positive ground.
The extra fuse isn't a safety feature – it further guards against the possibility of a short damaging your stepper motor supply. (Perhaps!)
Dave
…
Anyway, I don't know whether my power supply is earthed on the LT, but I know it's isolated (I made it). I can easily earth one side of the LT winding on the transformer. Is this the right thing to do? Seems to me that if it's floating I can't get any leakage to earth. There is already a big fuse to limit current from the power supply, I was just going to put the fuse in to protect the LED wiring, not me, I think I'm reasonably safe at 40v
Edited By duncan webster on 01/07/2016 13:51:10
Hi Duncan,
Your modification pretty much eliminates the mains risk inherent in the lamp as bought and I'd be happy to use it as is. So we're only worrying about the possibility of a low voltage short in the goose-neck if your lamp happens to have the same fault as suspected in MikeP's unit.
Where the fuse or fuses go depends on how your 40V stepper supply is configured. If you have a voltmeter, all you need to do to find out is to check if there are any volts between the machine ground and the plus and minus 40V stepper power wires.
If the 40V+ wire shows volts relative to machine ground, you need a fuse in the positive wire.
If the 40V- wire shows volts relative to machine ground you need a fuse in the negative wire.
If both + and – shows volts relative to machine ground, you need a fuse in both wires.
If neither shows volts relative to machine ground, the one fuse should be fine.
Does the Duffer know what he's talking about? My understanding comes from a lifetime interest in Amateur Radio where there are different earth requirements for Radio Frequencies, Mains Safety, lightning protection and signal isolation. Professionally I know a bit about electrical practice in computer rooms and data centres but note all that's theoretical and not particularly deep. Therefore I'm quite happy to be corrected about the advice I offer – several people on the forum are better qualified than me.
Cheers,
Dave