  • #229187
    Russell Eberhardt
    Participant
      @russelleberhardt48058
      Posted by Ajohnw on 09/03/2016 12:47:53:There is a catch however – motor cooling limits how slowly they can be run and significantly loaded for any length of time.

      Quite. For continuous use at half speed Marelli rate their inverter motors at about half power as a result of lack of cooling. In other words the same torque as at full speed. You can of course install an external electric fan to supplement cooling but I haven't found it necessary with my intermittent use.

      Best to retain the mechanical (belt or geared) speed change for times when you want extra torque.

      Russell.

      Advert
      #229188
      John Rudd
      Participant
        @johnrudd16576

        I think you will find that just putting your non Ex rated vfd into an ATEX approved enclosure isnt sufficient in terms of certified safety.

        The cert for the enclosure is purely for that, that is on its own with no added internals.

        To have the whole assembly certified costs a lot of money due to the testing needed to ensure the criteria are met.

        I know this as I work in the industry…and have gone down a similar route for some Ex rated equipment for a client.

        Best solution is mount your vfd as far as is practical from the booth, take into account cable lenghts etc..

        And if your motor/fan is mounted in the both it should be ATEX rated….

        Most of the above would apply to a business, in which case you may want to have a look at.      …http://www.hsa.ie/eng/Topics/ATEX_and_Electrical_Apparatus/Atex_Regulations_-_Frequently_Asked_Questions/

        If its a home job, then consider your own personal/ equipment safety….but you know that already…

        Edited By John Rudd on 09/03/2016 14:17:02

        #229194
        Martin Connelly
        Participant
          @martinconnelly55370

          Shaun, some invertors can be programmed with set points so once you find the speed for low flow a simple switch will select it. I think if you speak with some of the suppliers they will be able to suggest a suitable piece of equipment for your needs. It seems to me to be an easily implemented application for a VFD.

          Martin

          #229195
          duncan webster 1
          Participant
            @duncanwebster1

            In answer to RussB, I wouldn't be without the variable speed. I just leave the belt on middle speed and ramp it up and down with the VFD. Mitsubishi inverters have an output which you can just feed into a moving coil meter which tells you the % of top speed, so a simple table converts that to spindle RPM. Be careful as the output is at a highish voltage. Better is a tachometer gismo from e_bay, very cheap.

            I made my own tacho for the Centec as the pulley on the back is geared to the spindle so it had to have a factor in it to compensate

            Edited By duncan webster on 09/03/2016 14:43:37

            #229199
            Russ B
            Participant
              @russb

              John Rudd,

              Perhaps you're right, I don't work in electrical, (I'm in the Mechanical side of R&D)

              I would guess if we design a new product, its electrics are standardized by the electrical department and then they have that cabinet tested/approved for mass production etc Hence, I don't see that side of things – we just do as we're told =)

               

              Edited By Russ B on 09/03/2016 15:07:42

              #229201
              Martin Connelly
              Participant
                @martinconnelly55370

                I think it is a good application for a VFD. Many VFDs can be programmed with set point speeds so a simple switch would be all that is needed to go from full fan to low fan speed. I would suggest contacting some suppliers and asking for their recommendations.

                Martin

                #229203
                Ajohnw
                Participant
                  @ajohnw51620
                  Posted by Michael Briggs on 09/03/2016 13:51:28:

                  Hello John,

                  The device to fit between the VFD and motor to reduce noise is a three phase choke, that should iron out some of the harmonics from the output. They are primarily installed to reduce leakage on long cable runs that can cause false tripping.

                  Increasing the PWM frequency can also reduce noise in the motor. I have Allen Bradley drives installed on three machines, the motors do not make any discernible drive related noise.

                  I remember past VFD installations where the motors rang with a pretty unpleasant noise. I don't think it is as much a problem with modern devices.

                  Michael

                  Edited By Michael Briggs on 09/03/2016 13:55:33

                  Hi Michael. I could increase the switching frequency but was a bit concerned about eddy currents and bearings etc. Another thing they take care of on inverter rated motors which also have a separately powered cooling fan.. I knew they were chokes but haven't found anything suitable. On ebay at the moment there are some but these appear to be for noise reduction etc at 50 or 60Hz. My set up isn't as bad as some I have heard. The random switching helps a lot.

                  If anyone has any links to the correct beasts at reasonable cost I would be interested.I'd guess that the prices might be unreasonable in my case.

                  Noticing a comment about 1/2 speed half power same torque so power is reduced by the speed reduction take care that's how they all behave who ever makes them. The inverter messes with the voltage to contain the current to what it would be in normal use. Power is I^2 R so unfortunately heating effects are more or less the same and the fan is running at 1/2 speed. There must be some more due to eddy current losses in the magnetics too but it seems these can be disregarded. I do have a motor I intend to fit with a separate fan but as there is little need I don't want to risk it on my lathe. My DW mill doesn't need it as it's even easier to change speed.

                  Mentioning DW there was some one about who had phoned a supplier wanting to get rid of both pulley speed changes and the "back gear" in them. Supplier fine, fit one of my 2,800 rpm motors and one of my inverters and it will do what you want. There are a number about like this. Fortunately the punter found that TEK catalogue I mentioned and then got extremely annoyed saying inverters are hopeless etc. Prior to finding the catalogue he wasn't really prepared to accept what people told him concerning torque and heating effects.

                  John

                  #229205
                  Harry Wilkes
                  Participant
                    @harrywilkes58467

                    Hi Involute Curve

                    If the spray booth you refer to is in someone shed then what your suggesting is doggy to say the least, but if it's in an industrial environment then I suggest you you seek expert advice from someone who is conversant with electrical equipment in class 1/2 zones

                    H

                    #229218
                    Involute Curve
                    Participant
                      @involutecurve

                      yep it is a class 2 spray booth with water wash curtain and filtered incoming air, and air fed masks etc etc etc…… all electrical equipment is installed outside this booth, the inverter or VFD will be installed by a qualified electrician, the fan / motor was removed from a much larger booth the motor and fan are separated, hence the belt drive system, I just wanted a bit of advice on which type of VFD best suited this motor, (the 380V question was more a curiosity) in the past I've fitted VFD's to my lathes and milling machines but that's at home with single phase input supply, a simple reset of the jumpers and or resoldering the motors tails to Delta format inside the motor to suit this…………

                      anyhow thanks for the advice.

                      Shaun

                      #229222
                      Michael Briggs
                      Participant
                        @michaelbriggs82422

                        Hello John,

                        I would try to keep a change in switching frequency away from the limits of the settings to play safe. Allen Bradley recommend de rating the drive at higher frequencies.

                        I tried to paste a de rating graph but was told my posting was about 180,000 characters too long! Best to have a look at the manual for your drive.

                        If you get a situation where you think the motor has got too hot it may be better to run it unloaded and let the fan cool it rather than stop it dead.

                        A useful thing to do is set the drive display to indicate current for a while so you can see how the motor is being loaded.

                        Regards, Michael

                         

                         

                        Edited By Michael Briggs on 09/03/2016 18:04:55

                        #229225
                        Neil Wyatt
                        Moderator
                          @neilwyatt

                          The manual for my IMO cub has a little chart that says upping the frequency from 0.7 to 15kHz )(i.e. beyond what we more mature folk can hear) will: reduce noise, improve the current waveform, increase leakage current and increase electrical noise.

                          They then elucidate that lower frequency increases harmonic components of the output current waveform and increase the temperature of the motor, they say if driving at 0.75kHz, derate torque to 85%.

                          Raising the frequency increases power loss in the inverter, raising its temperature, but they state internal functions compensate and protect against this.

                          This would seem to suggest a middle-range frequency is a good start. The default is 1KHz,

                          It also has different sound tone settings that can reduce offensive noise without changing the frequency (if below 7khz) Guess this is similar to your random switching and uses asymmetric or irregular switching patterns.

                          Neil

                          #229226
                          Ajohnw
                          Participant
                            @ajohnw51620

                            I don't have a significant problem of any sort with my inverter set up but I'd love a link to a suitable choke to fit especially if it costed a tenner.

                            John

                            #229249
                            Hevanscc
                            Participant
                              @hevanscc

                              Got mine from Drives Direct, full story here http://www.model-engineer.co.uk/forums/postings.asp?th=112156

                              Hywel

                              Edited By Hywel Evans on 09/03/2016 23:08:55

                              #229258
                              MW
                              Participant
                                @mw27036

                                I wouldn't increase the maximum frequency, If possible, it's meant to run at it's default maximum for a reason, to ensure a long life. If your inverter also has a fan then this makes it a little easier to justify. If your simply increasing the frequency to ensure that the fan is up to speed, this isn't strictly necessary, you could always fit an additional independent fan onto the motor which can operate constantly regardless of your motor speed.

                                Michael W

                                #229344
                                Hollowpoint
                                Participant
                                  @hollowpoint

                                  Well I've been on a researching binge and it doesn't look at all difficult so I've gone ahead and ordered an inverter! I went with the invertek optidrive e3. Looks simple, lots of instructional videos on YouTube, fairly inexpensive and it's made in UK! I just hope I haven't overlooked anything?

                                  Motor: Brook Crompton, star or delta wiring, 3/4hp, 50hz, 2.4a, 1425rpm

                                  Inverter: Invertek Optidrive E3 0.75kW 230V 1ph to 3ph

                                  The only parts that looks tricky is the reversing switch, and I seem to have 3 white wires going into the motor? Not sure how I'm gonna know which is which?

                                  #229347
                                  Les Jones 1
                                  Participant
                                    @lesjones1

                                    You will not be using the reversing switch on the output of the inverter. The three wires from the motor go straight to the inverter output. It does not matter which way you connect them at first. If the forward and reverse are the wrong way round just swap over any two of the three wires. You will probably have to change the links in the motor connection box to change it from star to delta configuration. Post a picture of the connection box and members of this forum will tell you what to change. If you still want to use the old reversing switch it should be possible to use it to control the low voltage control signals to the forward and reverse control inputs on the inverter.

                                    Les.

                                    #229355
                                    Hollowpoint
                                    Participant
                                      @hollowpoint

                                      I understand the reversing switch just wires into the low power controls. It's the actual switch itself that looks a bit confusing (search santon rotary switch) I guess if I play around with a multimeter on the contacts I should be able to work it out?

                                      I think I have the motor delta wiring worked out, there is a diagram on the inside of the cover plate.

                                      That leaves me with the 3 motor input connections (and earth). On my motor these are marked A, B, C, N and all the wires are white. I'm not sure which way these need to be wired into the inverter output? They are marked U, V, W. And ground.

                                      #229361
                                      Les Jones 1
                                      Participant
                                        @lesjones1

                                        You should be able to identify the earth one easily either with a multimeter or where it is connected in the control box with the Santon switch. three of them will connect to the switch contacts and one to earth. Here is a diagram of one version of a Santon switch.

                                        contact_layout.jpg

                                        This switch was used for recersing a single phase motor but if it is the same as your switch it should help you work out how to connect it to the inverter control inputs.

                                        Les.

                                        #229370
                                        Hollowpoint
                                        Participant
                                          @hollowpoint

                                          This is a diagram of the wiring I found. So assuming my switch is similar to the above. I just connect:

                                          No.1 to terminal 3

                                          No.2 to terminal C

                                          No.3 to terminal A

                                          ??????

                                          #229377
                                          Les Jones 1
                                          Participant
                                            @lesjones1

                                            Yes, That should work. If You want to fit any interlocks or emergency stop buttons then just connect them all in series between terminal 1 on the inverter and terminal 3 on the switch. They all need to be normally closed contacts. I would have to see the manual on the inverter to see if this gave an NVR function. So it does not start up when mains is applied if the switch has been left in forward or reverse. I fitted start and stop buttons with my inverter as well as the reversing switch.

                                            Les.

                                            Edited By Les Jones 1 on 10/03/2016 19:14:01

                                            #229379
                                            Hollowpoint
                                            Participant
                                              @hollowpoint

                                              Great thanks that's very helpful! yessmiley

                                              Just need to figure out the motor connections now and then I'm sorted. Hopefully.

                                              #229465
                                              Hollowpoint
                                              Participant
                                                @hollowpoint

                                                The inverter arrived this morning! Need a little help. I've wired the motor in Delta as below. I now have motor terminals A, B, C but the motor output terminals on the inverter are marked U, V, W can someone tell me which motor to connect to each inverter terminal please?

                                                #229467
                                                John Rudd
                                                Participant
                                                  @johnrudd16576

                                                  HP,

                                                  If you have successfully wired your motor to DELTA, then connecting to the inverter is straight forward…..

                                                  Connect A,B and C to U,V and W….if the motor runs the wrong direction, swap any of the two phases over……

                                                   

                                                  Dont connect anything to the N connection.

                                                  Edited By John Rudd on 11/03/2016 15:27:51

                                                  #229478
                                                  Hollowpoint
                                                  Participant
                                                    @hollowpoint

                                                    Thanks, got it working now! laugh

                                                    #233062
                                                    Martin Newbold
                                                    Participant
                                                      @martinnewbold

                                                      Well done getting it running  I have just brought inverter and its arriving on Monday with a bit of luck, went for an ABB ACS150 – 0.37kw 230v . Have the motor wire coming as been told this is a must as it needs to be properly shielded. Will let you know how I get on. The reason for buying this one was it was the only one that actually stated it would work on a domestic supply . So figured as I had heard lots of stories with the inverters blowing domestic RCD I would go for this one. Will let you know how I get on.

                                                      Edited By Martin Newbold on 03/04/2016 11:15:41

                                                      Edited By Martin Newbold on 03/04/2016 11:19:13