Inverter drives for single phase motors

Advert

Inverter drives for single phase motors

Home Forums Help and Assistance! (Offered or Wanted) Inverter drives for single phase motors

Viewing 10 posts - 1 through 10 (of 10 total)
  • Author
    Posts
  • #404193
    Ed Dinning 1
    Participant
      @eddinning1

      Hi Gents, has anyone recommendations to make for the use of inverters on 230v. single phase, to run an induction motor(single phase, cap run, 230v); or have they successfully used them ?

      Maker, supplier, likely price ?

      A simple unit is all that is requires as the motor drives a fan and only 2 speeds are needed. One near max and the other about 1/2 speed.

      Many thanks, Ed

      Advert
      #33385
      Ed Dinning 1
      Participant
        @eddinning1

        Use of inverters with cap run induction motors

        #404203
        Tim Stevens
        Participant
          @timstevens64731

          I'm not sure what exactly you need to invert – the supply and the motor being both 230v single phase.

          Tim

          #404214
          John Haine
          Participant
            @johnhaine32865

            Ed wants to vary the speed, hence the frequency.

            Ed, I'm afraid that you are not likely to easily find an inverter for this job, as capacitor run motors have only a limited range of frequency over which the capacitor can maintain approximately a 90 degree phase shift. There has been some discussion on here about running a single phase motor without its capacitor on 2 phases from a VFD but I don't know if anyone has done it successfully. 2-phase inverters don't seem to be made.

            People do make fan speed controllers, whether they will work with your motor I don't know.

            **LINK**

            #404223
            Wout Moerman
            Participant
              @woutmoerman25063

              You want to use an inverter as a variable frequency drive? I don't know how much you can vary the frequency for a sine phase motor without it stopping. The capacitor is optimised for 50 or 60 Hz and I don't know if it generates a good phase shift at half the frequency.

              An alternative can be to remove the capacitor and power the motor as a 3 phase. For some single phase motors this is possible. Not if it starts with a centifugal switch I think. But if it has 3 identical windings it is possible. Then power it with a 1 to 3 phase VFD.

              #404230
              Ed Dinning 1
              Participant
                @eddinning1

                Hi Gents, thanks for the inputs.

                The application is a forced draught fan for a wood burning boiler.

                Original equipment is a 250w cap run induction motor that is working well. It originally used an Italian made inverter as a 2 speed VFD.#This has died with no obvious faults and no way to get a schematic.

                The PCB logo is (RD)² . It appears to have many more facilities for control than were needed, but no details of how to activate them so we can have full speed and about 1/2 speed,

                I've since found Invertek drives and their Optidrive range has a single phase in, single phase out inverter for fan and pump use that can be configured as I need it, as well as many other features that I will never use.

                Anyone familiar with this unit ?

                Ed

                #404243
                Anonymous
                  Posted by Ed Dinning 1 on 08/04/2019 19:18:23:

                  Anyone familiar with this unit ?

                  No but you need to be certain what sort of motor you have. The Invertek single phase in and out are intended for permanent split capacitor or shaded pole motors. Shaded pole motors in particular are used for fan applications as they are cheap and robust and the poor starting torque is not a problem. In addition the locked rotor currents are only 20% or so above rated current.

                  Andrew

                  #404259
                  norman royds 2
                  Participant
                    @normanroyds2

                    I have a brook Crompton parkinson range mater inverter v220/240 input output 370 w I bought board with dc controller and a single phase inverter and single to 3phase so do not know what it was for but it looks very complex for a fan regards norm hope this helps you

                    #404328
                    Ian S C
                    Participant
                      @iansc

                      Some two speed fans of around 40 Watt use a filter choke as found in older power supplies, when that is switched in the speed drops, 20/25 % at a guess. I would have thought that being able to switch the motor from 2 pole to 4 pole to adjust speed.

                      Ian S C

                      #404338
                      Russ B
                      Participant
                        @russb

                        Ed,

                        How about using a 110v transformer and a rotary switch to run through the 110v or bypass it. This keeps your CAP running at the correct frequency for the phase shift