      Hi guys & gals. I am looking for a used 240v to 3 ph inverter to do a complete series on how to connect a 3 phase motor to a single phase inverter. To the hams a (VFD) Anything around 0.38kw to 0.5kw will do the job. This is because i have a spare 0.38 kw motor & have been asked by quite a few people to do this video for them. Larger i suppose would do too. This will include how to make a small control panel to use with it if required. I had lots of these when i retired & foolishly sold them at car booties for next to nothing.

      As everyone knows this would be quite volotile to post on this forum. But i am going to at some point. For the Rocket scientist's out there please do not comment. I have had a lot of interest from my subscribers to do this because it frightens the living daylights out of some guys when the word 3 phase is mentioned.

      This will be from safely using the correct type of cheaply obtainable terminals . To connecting correctly. To using the proper type of SY cable . Earthing will be important. Do i need a remote panel as lots of folk say yes. No you do not. Some question asked were can i switch the inverter from forward to backward without causing damage. The answer is of course you can many time a minute. Me & my company built many control panels that required a piece of equipment to run back & forth at different speeds. I designed in autocad & priced +built many of these such panels. They ran for many years with little or no trouble.

      When i eventually do this series, all i ask is that a few members refrain from negative comments which will spoil it for the many that will benefit from my experience. commenting which usually gets the thread deleted. Just the the 3 of you. As I know you 3 are superior to to anyone else on the forum & would spoil what could be a learning curve to those who fear fitting a new motor to there machine.

      There are more than you think. Don't be afraid guys it is very easy & after a little bit of programming which SOD, Robert & NDIY will walk you through will run perfectly. Keep an eye out for the vid.

      Steve.

      Advert
      #37097
      Steviegtr
      Participant
        @steviegtr

        Setting up a inverter.

        #628405
        Neil Wyatt
        Moderator
          @neilwyatt

          Steve, I'm not sure sarcasm is the most effective way of avoiding argument.

          There's no issue about discussing 3 phase on the forum. My own article::

          http://www.model-engineer.co.uk/news/article/3-phase-conversion-and-other-alternative-methods-of-powering-a-mini-lathe/18752

          But obviously, people should only work with mains voltages if they are competent to do so.

          One area that will always be one of contention is proper shielding for RFI – not helped by some manufacturer's guidance being completely contradictory to that of other manufacturers.

          Neil

          #628406
          Steviegtr
          Participant
            @steviegtr
            Posted by Neil Wyatt on 10/01/2023 00:32:23:

            Steve, I'm not sure sarcasm is the most effective way of avoiding argument.

             

            There's no issue about discussing 3 phase on the forum. My own article::

            http://www.model-engineer.co.uk/news/article/3-phase-conversion-and-other-alternative-methods-of-powering-a-mini-lathe/18752

            But obviously, people should only work with mains voltages if they are competent to do so.

            One area that will always be one of contention is proper shielding for RFI – not helped by some manufacturer's guidance being completely contradictory to that of other manufacturers.

            Neil

            Point taken. Maybe not post it here when done. 

            Steve.

            Edited By Steviegtr on 10/01/2023 00:41:59

            #628427
            Oldiron
            Participant
              @oldiron
              Posted by Steviegtr on 10/01/2023 00:40:56:

              Posted by Neil Wyatt on 10/01/2023 00:32:23:

              Steve, I'm not sure sarcasm is the most effective way of avoiding argument.

              There's no issue about discussing 3 phase on the forum. My own article::

              http://www.model-engineer.co.uk/news/article/3-phase-conversion-and-other-alternative-methods-of-powering-a-mini-lathe/18752

              But obviously, people should only work with mains voltages if they are competent to do so.

              One area that will always be one of contention is proper shielding for RFI – not helped by some manufacturer's guidance being completely contradictory to that of other manufacturers.

              Neil

              Point taken. Maybe not post it here when done.

              Steve.

              Edited By Steviegtr on 10/01/2023 00:41:59

              Was going to comment on this but thought better of it. (for the good Steve) smiley

              regards

              #628432
              Mike Poole
              Participant
                @mikepoole82104

                I think CY cable should be used for screening, SY is a mechanical protection braid.

                Mike

                #628446
                john fletcher 1
                Participant
                  @johnfletcher1

                  I've read a lot about a competent person, out of interest try to find out how one actually becomes a competent person be it gas or electricity Give your self plenty of time. John

                  #628474
                  Martin Connelly
                  Participant
                    @martinconnelly55370

                    John, I always had similar thoughts about the Authorised Personnel Only signs that cropped up regularly. I argued that anyone can deem themselves authorised in their own mind. The same goes for competent without some definition of what is meant by competent.

                    Martin C

                    #628476
                    noel shelley
                    Participant
                      @noelshelley55608

                      Having writen an article for ME sometime ago, and having seen how some will split hairs or require the highest standards of safety or professional knowledge even in the hobby field I felt that It was better for all concerned that I do not submit it for publication, even though it involved voltages below 20v. It had been written on the assumption that the reader was an inteligent being – may be a dangerous assumption !

                      After the Chinese Diesel Heater episode I would be very wary of bothering Steve ! There are some here who know so much that even when the facts are looking them in the face still insist their right !

                      Good Luck. Noel.

                      #628477
                      John Haine
                      Participant
                        @johnhaine32865
                        Posted by john fletcher 1 on 10/01/2023 10:52:15:

                        I've read a lot about a competent person, out of interest try to find out how one actually becomes a competent person be it gas or electricity Give your self plenty of time. John

                        I guess that the electrician who wired our immersion heater to the lighting circuit, and his apprentice who buried an LED power supply puck inside the loft insulation so that it overheated and burned out, would claim to be "competent persons". Frankly I thought they were a walking menace to the public.

                        #628486
                        SillyOldDuffer
                        Moderator
                          @sillyoldduffer
                          Posted by john fletcher 1 on 10/01/2023 10:52:15:

                          I've read a lot about a competent person, out of interest try to find out how one actually becomes a competent person be it gas or electricity Give your self plenty of time. John

                          Easier to identify incompetent persons, but even they get away with murder! And then despite obviously questionable results incompetents often attract bands of loyal followers. It's a funny old world.

                          Dave

                          #628488
                          Dave Halford
                          Participant
                            @davehalford22513

                            Competent person? That would be covered here so it seems to be not so woolly after all. Says the man who was a competent person to fit a 13A plug and had a card to prove it. Yes really!

                            With RFI you may get trouble if the VFD spec says apply RFI controls and you don't and someone complains. If it's not mentioned then you can shrug I guess. There was an RFI issue at Heathrow due to someone unplugging a live CATV feed in a Brentford flat and screwing up aircraft on approach flying straight down the Brentford main drag, as they do.

                            #628497
                            Emgee
                            Participant
                              @emgee
                              Posted by John Haine on 10/01/2023 12:54:51:

                              I guess that the electrician who wired our immersion heater to the lighting circuit, and his apprentice who buried an LED power supply puck inside the loft insulation so that it overheated and burned out, would claim to be "competent persons". Frankly I thought they were a walking menace to the public.

                              John, if you haven't found an electrician yet use the following link, just enter you postcode to have a choice of NICEIC registered persons/firms in your area.

                              **LINK**

                              Emgee

                              #628499
                              Harry Wilkes
                              Participant
                                @harrywilkes58467

                                Steve do yourself a favour post it on youtube because they'll pick it to pieces frown

                                H

                                #628519
                                Oldiron
                                Participant
                                  @oldiron
                                  Posted by Harry Wilkes on 10/01/2023 15:00:20:

                                  Steve do yourself a favour post it on youtube because they'll pick it to pieces frown

                                  H

                                  Looks like the haters have already started. Not sure I want to be on this forum. Will have to give it some serious thought.

                                  regards

                                  #628523
                                  Robert Atkinson 2
                                  Participant
                                    @robertatkinson2

                                    1/ If this is for youtube, ask your subscribers to give you a VFD.
                                    2/ A used VFD is a bad idea. Firstly it may have a fault or fault(s) that could be intermittent or unusual settings that cause trouble. Secondly it may be older model no longer available.
                                    3/ A control panel IS required, remote or on the box the VFD is in. The controls on the front of VFDs are for set-up and test, not routine operation. and you can't get at them without opening the enclosure. You will be putting it in an enclosure won't you?

                                    If you post here or on youtube any registered user can comment. its part of the process….

                                    Robert G8RPI.

                                    Edited By Robert Atkinson 2 on 10/01/2023 17:31:44

                                    #628525
                                    John Haine
                                    Participant
                                      @johnhaine32865
                                      Posted by Emgee on 10/01/2023 14:43:21:

                                      Posted by John Haine on 10/01/2023 12:54:51:

                                      I guess that the electrician who wired our immersion heater to the lighting circuit, and his apprentice who buried an LED power supply puck inside the loft insulation so that it overheated and burned out, would claim to be "competent persons". Frankly I thought they were a walking menace to the public.

                                      John, if you haven't found an electrician yet use the following link, just enter you postcode to have a choice of NICEIC registered persons/firms in your area.

                                      **LINK**

                                      Emgee

                                      Thanks but this was several years back. I'm sure the firm was registered, my point was that they were incompetent.

                                      #628526
                                      peak4
                                      Participant
                                        @peak4
                                        Posted by Dave Halford on 10/01/2023 14:18:50:

                                        Competent person? That would be covered here so it seems to be not so woolly after all. Says the man who was a competent person to fit a 13A plug and had a card to prove it. Yes really!

                                        ………………….

                                        Yes I did a full day's internal works course for that myself, and came away with the relevant certificate.
                                        The very last part of the course covered that we were now not allowed to insert the plug into a socket, until we had booked an appointment, travelled to a different location and had it PAT approved by our local tester.

                                        Someone on high had deemed it ridiculous that us engineers couldn't fit a plug, but hadn't quite thought it through.

                                        Similarly the testing engineer was told that any mains equipment, not supplied via our official stores catalogue, must have the plug cut off and be skipped, other wise he would be formally disciplined as breaching the company's H&S rules; He then pointed out that would also include his PAT machine.
                                        Ho Hum.

                                        Bill

                                        Edited By peak4 on 10/01/2023 17:33:59

                                        #628527
                                        Robert Atkinson 2
                                        Participant
                                          @robertatkinson2

                                          Going off topic, but one issue with the registration route like NEC-EIC is that only ONE employee needs to go through the registration process. They can then, if they wish, delegate the authorty to do the work to others. They do of course remain responsible but it seems some don't realise this or just don't care as long as they make money.

                                          For electrical work, including "Part P" you don't have to registered or have any qualifications. Though in that case you would have to convince the building inspector that you are competent (accepting anything less than the usual qualifications is entrely up to them and why should they?) and then pay their fees to record the work. This is not normally cost effective.

                                          Robert G8RPI.

                                          #628528
                                          Chris Pearson 1
                                          Participant
                                            @chrispearson1

                                            I am struggling to see the point of the OP. Is it to cadge a VFD, gauge opinion, or a combination of the two?

                                            There is no need to be a registered competent person because that is to do with fixed wiring. (I was one once.)

                                            It really is a matter of following the manufacturers' instructions and tidy workmanship.

                                            #628531
                                            Nigel Graham 2
                                            Participant
                                              @nigelgraham2

                                              Don't let the "haters" get to you – nor wind 'em up by calling them that.

                                              Nevertheless…

                                              If you are installing anything electrical in your workshop for hobby use, only you need and can judge if you are "competent" within the meaning of… but it is wise to consider your abilities very carefully. If any doubt find a reputable electrician, preferably with industrial wiring knowledge; although the task is not technically difficult if you are using a purchased, complete set provided with the circuit-diagram and instructions.

                                              I have fitted 3ph conversion sets to four machines: a Harrison L5 and a Myford ML7 lathes, a Myford VMC mill and a BCA jig-borer; but for each case bought an appropriate motor and electronics set (Newton-Tesla) having told them for which machine; and I followed their instructions very carefully. Though my years of specialist electrical and electronic assembly work did help me..

                                              The ML7's electronics are manufactured as self-contained in a single box I could screw to the cabinet, with a simple shield over it. For the other machines I placed the inverters well away from the moving parts and swarf, with the important point about thinking where to put the controls. (They are in separate units.)

                                              That for the Harrison lathe is above the tailstock, within reach when standing in the normal spot, but needing my arm move away from the chuck to use it. Though I still need use the clutch lever in its horrible designed place above the headstock!

                                              '

                                              One important point. Motor speed!

                                              The motor still needs run fast even if you want the chuck to rotate slowly, so don't be swayed by those who advocate throwing the machine's pulleys and belts or gearbox away! It allows maximum torque and slow cutting speed / feed without over-heating the motor by its fan barely spinning – I am not sure if there are other potentially deleterious effects.

                                              The controller on the N-T sets has its red sector at low, not high speed.

                                              .

                                              I find using the ML7's direct drive on the middle and low spindle pulleys covers most turning, back-gear for screw-cutting or as otherwise applicable , without stressing the well-shielded motor.

                                              The L5's spindle speed is around 60-70rpm in lowest gear with the 3ph motor, on a frame above the headstock, happy at around 900+ rpm, according to the controller scale.

                                              The milling-machine still has its 2-stage belt and pulley arrangement, and that will stay despite being awkward to use, unless I can design some better system. Or more accurately, physically make it…

                                              The BCA is a fast-running machine anyway so the existing belt drive from the replacement 3ph motor is fine.

                                              I am recommissioning a small horizontal mill (Denbigh H4) but will stick to simple 1-phase motor and mechanical transmission for that. It does not need anything sophisticated. In fact only today I collected a mechanical variable-ratio drive to use on it, from a private-seller advertising on this very Forum!

                                              #628551
                                              Emgee
                                              Participant
                                                @emgee
                                                Posted by Robert Atkinson 2 on 10/01/2023 17:46:06:

                                                Going off topic, but one issue with the registration route like NEC-EIC is that only ONE employee needs to go through the registration process. They can then, if they wish, delegate the authorty to do the work to others. They do of course remain responsible but it seems some don't realise this or just don't care as long as they make money.

                                                Robert G8RPI.

                                                If you can provide evidence of non compliant with regulations work carried out by any NICEIC member in the interest of safety you as a professional engineer should report it to the relevant body.

                                                Emgee

                                                #628552
                                                Emgee
                                                Participant
                                                  @emgee

                                                  On the subject of location of any VFD used to control a motor I am surprised that some haven't vilified Les for his installation on the drill pictured in another thread.

                                                  Emgee

                                                  #628562
                                                  Robert Atkinson 2
                                                  Participant
                                                    @robertatkinson2
                                                    Posted by Emgee on 10/01/2023 20:26:03:

                                                    Posted by Robert Atkinson 2 on 10/01/2023 17:46:06:

                                                    Going off topic, but one issue with the registration route like NEC-EIC is that only ONE employee needs to go through the registration process. They can then, if they wish, delegate the authorty to do the work to others. They do of course remain responsible but it seems some don't realise this or just don't care as long as they make money.

                                                    Robert G8RPI.

                                                    If you can provide evidence of non compliant with regulations work carried out by any NICEIC member in the interest of safety you as a professional engineer should report it to the relevant body.

                                                    Emgee

                                                    If I did I would. As you say I have a professional obligation. Everyone has a a moral obligation to do so.

                                                    #628590
                                                    Steviegtr
                                                    Participant
                                                      @steviegtr
                                                      Posted by Harry Wilkes on 10/01/2023 15:00:20:

                                                      Steve do yourself a favour post it on youtube because they'll pick it to pieces frown

                                                      H

                                                      Agree. Pretty much in the background now.

                                                      S.

                                                    Viewing 25 posts - 1 through 25 (of 32 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Home Forums The Tea Room Topics

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up