Posted by Chris Pearson 1 on 19/09/2023 22:59:36:
Well yes.
If we exclude an (earth) fault and inrush, what is left?
Some readings on the circuits would be useful, but I'm not sure nowadays if an insulation-resistance test can be performed whilst LED lights are connected. Needs an Electrician ideally to assess this.
Other things to check:
– With the incoming power off and everything made safe I would check that the MCB's are properly secured to the busbar in the consumer unit and the circuits are also tightly connected in the MCB's. Might be a loose connection and/or corrosion build-up.
– Swap the inside and security light circuits onto each other's MCB's. If the security lights then start to trip, it could be a faulty MCB.
– Check the connections to each of the light fittings are sound and make good where necessary. See over time if this has sorted the problem. There might be a dodgy connection on both runs of lights. Some of the push-in types of connectors aren't that great in my opinion, if these are what're used, but I doubt this is the issue. Worth checking anyway.
Ed.