  • #245152
    Speedy Builder5
    Participant
      @speedybuilder5

      I can't work out why the RCD on the outside lantern light keeps tripping. I have good earth around all the wires. The insulation is ANTI this and ANTI that, so it should be OK. What does the team think ?
      BobH

      antiearth.jpg

      Advert
      #34698
      Speedy Builder5
      Participant
        @speedybuilder5

        RCD trips out

        #245154
        Ed Duffner
        Participant
          @edduffner79357

          smiley That's a lot of wires for a lantern Bob, PIR detector?

          Rinse and repeat, with the electric off, then dry fully.

          Ed.

          #245159
          Speedy Builder5
          Participant
            @speedybuilder5

            Yep, 2 earths, one to the lamp socket and the other to the cast aluminium lantern plus loop off to the next lamp – 3 lamps in parallel. Cut off the old terminal block off and replace.

            #245161
            SillyOldDuffer
            Moderator
              @sillyoldduffer

              Hmmm, tricky one. Might be an earth leak…

              #245165
              Neil Wyatt
              Moderator
                @neilwyatt

                Looks well 'earthed' to me

                Is it anti-ant?

                Is the brown wire intact? Looks like it could be damaged to me.

                Neil

                #245169
                Speedy Builder5
                Participant
                  @speedybuilder5

                  No, there is plenty of earth. Brown wire cut back to good. It is surprising just what damage ants and other critters can do. Both ends of the conduits were sealed around the cables – but they still got in and made their home there.

                  #245171
                  Neil Wyatt
                  Moderator
                    @neilwyatt
                    Posted by Speedy Builder5 on 02/07/2016 19:04:58:

                    No, there is plenty of earth.

                    That was my (humorous) point!

                    Neil

                    #245182
                    SillyOldDuffer
                    Moderator
                      @sillyoldduffer

                      Now I'm confused! I thought we were all joking…

                      Cheers,

                      Dave

                      #245188
                      DMB
                      Participant
                        @dmb

                        Its all the muck in the casing.When it gets damp, it shorts the connections.
                        Worthing club had same trouble with signalling failure. Pesky ants built nest in connections box under track.

                        #245204
                        Colin Whittaker
                        Participant
                          @colinwhittaker20544

                          Guys,

                          A good earth keeps you safe. It doesn't prevent RCCB trips.

                          The RCCB (residual current circuit breaker) looks for an imbalance in the live and neutral line currents (due to a >30mA leak) and trips the breaker.

                          With the power off, wash, clean, dry and you should be good, as long as the cable isn't damaged elsewhere.

                          Colin

                          #245206
                          Clive Hartland
                          Participant
                            @clivehartland94829

                            Perhaps get some adhesive heat sealing tube and completely seal all the connections and joints.

                            Clive

                            #245208
                            MW
                            Participant
                              @mw27036

                              If it was working well prior to this then maybe some damage has occured or damp is shorting it, outdoor electrics are a pesky business.

                              Or, perhaps you put something new on the line and the wires are overheating, depends what they're rated for, i'm not saying this is the case just i had a couple of garage lights kept shorting because the copper was too thin.

                              Michael W

                              Edited By Michael Walters on 03/07/2016 09:06:07

                              #245220
                              Speedy Builder5
                              Participant
                                @speedybuilder5

                                I started this post off, a bit tongue in cheek, but mainly to show how ants and other creatures work to confound our futile attempts to "improve" the world we live in.
                                The problem has been sorted, tested and as far as I am concerned, safe to use once again. I am sure that if the wiring survives for another 10 years, I will have had my moneys worth. I expect the lanterns will have to be replaced some time as its a big ask for die cast Aluminium to survive 20 years in an outdoor environment and in any case they should perhaps be replaced with LEDs or whatever new technology is around the corner.
                                Thanks for all the suggestions guys (and girls).
                                Over and out
                                BobH

                              Viewing 14 posts - 1 through 14 (of 14 total)
                              • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                              Advert

                              Latest Replies

                              Home Forums The Tea Room Topics

                              Viewing 25 topics - 1 through 25 (of 25 total)
                              Viewing 25 topics - 1 through 25 (of 25 total)

                              View full reply list.

                              Advert

                              Newsletter Sign-up