cable core colours for 3 phase motors

Advert

cable core colours for 3 phase motors

Home Forums Manual machine tools cable core colours for 3 phase motors

Viewing 25 posts - 1 through 25 (of 40 total)
  • Author
    Posts
  • #614031
    gerry madden
    Participant
      @gerrymadden53711

      I intend to replace the cable on my J&S grinder motors. The existing ones (or certainly the sheathing) is hard enough to crack when bent, probably from oil and ageing.

      The colour coding on the existing cables is three browns and a yellow/green earth. (This last one is a true earth, fixed to the casing, not a neutral.) I can't seem to find this spec anywhere and I suspect that's because the regulations have changed. Can anyone advise me what combination I should be installing now please?

      Also, my preference is for rubber sheathing for oil resistance and flexibility. Am I being a bit old fashioned ?!

      Advert
      #14661
      gerry madden
      Participant
        @gerrymadden53711
        #614033
        roy entwistle
        Participant
          @royentwistle24699

          I wouldn't consider rubber to be oil resistant. In fact I'd be surprised if you can still get it. Google will give you the current colour codes

          #614037
          SillyOldDuffer
          Moderator
            @sillyoldduffer

            Old-style rubber best avoided even if you can find some. It goes hard, cracks and the insulation falls off. Not good with heat and not really oil resistant. Silicone rubber is OK though.

            The colours don't matter much because there's no need to distinguish between phases. When flexible wires are used, one of the conventions is Brown, Brown, Brown. Another is Red, Yellow, Blue.

            Non flexible cable usually Red Yellow Blue or Red White Blue.

            Dave

            #614038
            Anonymous

              The UK harmonised standard is brown, black and grey for phases, blue for neutral and yellow/green for earth.

              Andrew

              #614040
              Pete Rimmer
              Participant
                @peterimmer30576
                Posted by SillyOldDuffer on 18/09/2022 14:53:58:

                Old-style rubber best avoided even if you can find some. It goes hard, cracks and the insulation falls off. Not good with heat and not really oil resistant. Silicone rubber is OK though.

                The colours don't matter much because there's no need to distinguish between phases. When flexible wires are used, one of the conventions is Brown, Brown, Brown. Another is Red, Yellow, Blue.

                Non flexible cable usually Red Yellow Blue or Red White Blue.

                Dave

                Red Black Blue went out more than 15 years ago. Now it's Brown Black Grey.

                #614041
                Dave T
                Participant
                  @davet19446

                  Red, Blue, Yellow phase colours went out more than 15 years ago. Now it's Brown Black Grey.

                  Edited By Dave T on 18/09/2022 15:10:42

                  #614046
                  Phil Whitley
                  Participant
                    @philwhitley94135

                    red yellow blue went out when we were persuaded to harmonise with the EU, who have a very sketchy standard of electrical safety anyway, still using unshuttered sockets, which we changed in 1947!! Now we are no longer in the EU we should go back, but for the fact that brown grey black are easier for colour blind electricians to recognise. Having said that colour blindness and electrical engineering hardly go together even though my dad was both!

                    #614050
                    SillyOldDuffer
                    Moderator
                      @sillyoldduffer
                      Posted by Pete Rimmer on 18/09/2022 15:04:25:

                      Posted by SillyOldDuffer on 18/09/2022 14:53:58:

                      Old-style rubber best avoided even if you can find some. It goes hard, cracks and the insulation falls off. Not good with heat and not really oil resistant. Silicone rubber is OK though.

                      The colours don't matter much because there's no need to distinguish between phases. When flexible wires are used, one of the conventions is Brown, Brown, Brown. Another is Red, Yellow, Blue.

                      Non flexible cable usually Red Yellow Blue or Red White Blue.

                      Dave

                      Red Black Blue went out more than 15 years ago. Now it's Brown Black Grey.

                      Oh dear. There's no doubt now that I've passed my "Best Before" date…

                      sad

                      #614051
                      Robert Atkinson 2
                      Participant
                        @robertatkinson2

                        The current best practice cable for this application would be "SY" 4 core (3 + PE) e.g.

                        https://www.tlc-direct.co.uk/Products/MF1dot5slash4.html.

                        The phase colour code is for supplies. Ideally it should not be used on a motor that might be reversed. The SY cable linked to has one Green/Yellow for the Protective Earth (PE) and 3 blacks which have numbers printed on them.

                        Robert G8RPI.

                        #614053
                        Mike Poole
                        Participant
                          @mikepoole82104

                          HOFR cable is not hard to find and is a rubber type cable that is Heat Oil Flame Retardant hence HOFR. I doubt that it is a natural rubber to meet that requirement but it is nicer than PVC cable for power tool flex.

                          Mike

                          #614055
                          Steve Neighbour
                          Participant
                            @steveneighbour43428
                            Posted by Dave T on 18/09/2022 15:09:43:

                            Red, Blue, Yellow phase colours went out more than 15 years ago. Now it's Brown Black Grey.

                            Edited By Dave T on 18/09/2022 15:10:42

                            Only for Low Voltage !! (0 – 1,000 volts) anything higher in the UK is still Red Yellow Blue – thankfully

                            It was the most by most ill thought through changes that happened in Electrical Engineering it causes all sorts of issues when connecting 'new' to 'old'

                            Old Harmonised

                            Red = Brown (L1)

                            yellow = Black (L2)

                            Blue = Grey (L3)

                            Black = Blue (N)

                            No prizes for spotting where the mistakes can creep in !!!

                            (Yet another example of the EU imposing a change on the UK that was stupid !!)

                            #614058
                            Clive Foster
                            Participant
                              @clivefoster55965
                              Posted by Robert Atkinson 2 on 18/09/2022 16:07:40:

                              The current best practice cable for this application would be "SY" 4 core (3 + PE) e.g.

                              https://www.tlc-direct.co.uk/Products/MF1dot5slash4.html.

                              The phase colour code is for supplies. Ideally it should not be used on a motor that might be reversed. The SY cable linked to has one Green/Yellow for the Protective Earth (PE) and 3 blacks which have numbers printed on them.

                              Robert G8RPI.

                              Does anyone know the reasoning behind the 3 blacks for phase power idea. Seems potentially dangerously confusing to me. Especially when done with 3 unidentified single cores pulled through conduit. Back in the day 3 red singles seemed to be common for factory et al installations.

                              My workshop is single core in conduit but its all brown, black, grey connected to the L1, L2 and L3 outputs of the phase converter with blue for neutral. So everything is the same. If any motors ran backwards I changed the internal motor connections, not the supply cables, making sure the control gear followed the same conventions and was laid out as per the wiring diagram in the manual.

                              I can do without surprises like things starting up backwards if plugged into a different socket for any reason. All my machines connect via 5 way fully populated plugs and socket with a proper lever disconnector immediately upstream of the socket. I may not currently have anything that needs the neutral connector but its there, properly connected and ready to go. Proper connection and safe termination of anything to do with 240 / 440 volts is a religious matter for me!

                              I use the bright yellow Lewden disconnectors with the big red lever so I can see right across the workshop if something is on or off. Having a plug on the machine lead means that I can simply pull the plug if I really, really want to be sure something is off.

                              Have absolutely zero desire to verify that getting tangled up in something spun by a 3 hp motor hurts. My imagination will do just fine thanks!

                              Clive

                              Edited By Clive Foster on 18/09/2022 16:38:15

                              #614062
                              David George 1
                              Participant
                                @davidgeorge1

                                I have used SY cables for many power supply connections and are my preferred connection cable especially where there is possibility of movement. There are many sizes of cable with many numbers of cores but all have an extra layer of protection with a braided steel sheaf in the middle which is earthed with the correct cable gland as extra protection and the cable is not affected by oil etc. Every core is numbered its full length and it is easy to attach a rubber or shrink tube sheaf to each core if you wish to code by colour.

                                David

                                #614063
                                DC31k
                                Participant
                                  @dc31k
                                  Posted by Clive Foster on 18/09/2022 16:36:40:

                                  Does anyone know the reasoning behind the 3 blacks for phase power idea.

                                  If you dig into it, SY cable is not certified for power supply. It is for use as a control cable only. If you buy 24 core SY cable, it will have 23 black conductors labelled from 1-23. The numbers are printed about every 4" on the cable so difficult to be confusing.

                                  I think the proper cable to be used for power supply is H0xRN-F, where x is most commonly 5 or 7 (hundred volts).

                                  See, for example:

                                  https://uk.rs-online.com/web/generalDisplay.html?id=ideas-and-advice/sy-cable-guide

                                  SY is popular as a power cable as it is cheap and robust, but technically it is incorrect.

                                  #614064
                                  Pete Rimmer
                                  Participant
                                    @peterimmer30576

                                    Yes there is a problem wit SY not complying with BS-something or other. Have no fear though it is plenty good enough for power supplies we have been using it up to 100A for our mobile plant at work now for at least 25 years, all in extreme duty situations. It's very robust.

                                    Only just recently have we had an issue with a main contractor insisting we use HO7RN cables instead of SY, and that was only because of an audit.

                                    #614067
                                    Robert Atkinson 2
                                    Participant
                                      @robertatkinson2

                                      Most SY cables are appropriately approved. The X cores in black +PE SY cables are not suitable for 230V flexible leads for direct connection to single phase mains, but only because they don't comply with the colour code. You can get 2+PE SY cables that are Brown, Blue & Yellow/Green (and 3 phase colours) and fully compliant.
                                      For connecting between switch gear and a motor the numbered black core + green/yellow is fully compliant. It is also as I stated earlier, incorrect to use the 3 phase colour code between switchgear and motor when the motor is reversable because in at least one direction the colours will be wrong.

                                      https://www.clevelandcable.com/SY-control-flexible-cable-pvc-up-to-95mm/

                                      The use of a single colour in conduit is purely down to cost. It costs more to stock 4 or 5 colours than two or three.

                                      Robert G8RPI.

                                      Edited By Robert Atkinson 2 on 18/09/2022 18:27:51

                                      #614068
                                      gerry madden
                                      Participant
                                        @gerrymadden53711

                                        Thanks chaps for all your input. Your comments have helped me navigate the web more efficiently and now I know hugely more about the subject than I did 4 hours ago. I've also just placed an order for a cheap chunk of H07RN-F, and with no delivery charges which is always nice!

                                        The SY cable is attractive but seemed to have a thicker OD than the H07 for the same wire size. I guess that's to do with the internal braiding. I thought that might compromise its flexibility a little, but I may be wrong. Sometime I'll get a small piece and see – nothing like hands on. Perhaps because SY is not officially for 'power' applications, it didn't have the correct BROWN BLACK GREY core colours as mentioned by Andrew J. Not that this is hugely important, just nice to have some order in life

                                        Gerry

                                        ps, Just noticed from Roberts latest link that the SY can have the 'correct' colour codes (described as 'also available' ) Nothing is ever certain in life is it

                                         

                                        Edited By gerry madden on 18/09/2022 18:39:16

                                        Edited By gerry madden on 18/09/2022 18:40:05

                                        #614081
                                        Master of none
                                        Participant
                                          @masterofnone

                                          BS 7671 requires that the cables comply with relevant standards which could be British Standards or equvalent. SY cable does not have a particular standard. However it is widely used in industry for final connections to machines where inverters (VFDs) are used to control motors. The reason is that the braid on ST cable is earthed and helps to minimise the noise caused by the VFD which could affect other equipment.

                                          SY is a useful cable but should not be considered as an armoured cable as the braid in not as tough as the steel wires in an SWA cable.

                                          Yes, the cores are all black and are numbered but coloured sleeve could be used to identify the cores as Brown, Black and Grey.

                                          Special brass cable glands are available terminating the cable but, in many cases, I have seen plastic stuffing glands used. It is important that the braid is earthed at the origin of the cable and that the terminations are not put under strain if the cable is pulled.

                                          Edited By Richard Taylor 17 on 18/09/2022 21:13:10

                                          #614084
                                          DC31k
                                          Participant
                                            @dc31k
                                            Posted by Richard Taylor 17 on 18/09/2022 21:12:51:

                                            SY cable does not have a particular standard.

                                            The reason is that the braid on SY cable is earthed and helps to minimise the noise caused by the VFD which could affect other equipment.

                                            Your statement contradicts the link posted above pointing to Cleveland Cables site where it says the cable is made to BS EN 50525-2-11.

                                            Your statement contradicts the link posted above to RS site where it says the correct cable to use if you want to minimise electrical noise is CY (not SY).

                                            You earth the braid on the cable so that if it is damaged and a live conductor from inside the cable touches the braid, it cannot become live and kill you if you touch it.

                                            #614089
                                            Jelly
                                            Participant
                                              @jelly
                                              Posted by DC31k on 18/09/2022 21:43:47:

                                              Posted by Richard Taylor 17 on 18/09/2022 21:12:51:

                                              SY cable does not have a particular standard.

                                              The reason is that the braid on SY cable is earthed and helps to minimise the noise caused by the VFD which could affect other equipment.

                                              Your statement contradicts the link posted above pointing to Cleveland Cables site where it says the cable is made to BS EN 50525-2-11.

                                              Your statement contradicts the link posted above to RS site where it says the correct cable to use if you want to minimise electrical noise is CY (not SY).

                                              You earth the braid on the cable so that if it is damaged and a live conductor from inside the cable touches the braid, it cannot become live and kill you if you touch it.

                                              The really important bit for people to know in all of this is that the braid is not sufficiently sized to act as the CPC (protective earth) and in addition to earthing the braid, a dedicated earth conductor must be provided in the cable itself.

                                              I have seen too many installs where it's been assumed that you can use the braid of SY in the same way as you can the armour in SWA.

                                              .

                                              In any case the use of SY (or other non-standard cables) is to be discouraged unless there's a good reason to do so (and in doing so deviate from BS7671), as documented by the designer of the installation.

                                              This document from Eland Cables explains the situation with respect to BS EN 50525-2-11 (which is a standard for how one makes cables generally, not a standard specifying the design of a particular type of cable) not translating into 18th edition compliance without further consideration.

                                              Edited By Jelly on 18/09/2022 23:49:33

                                              #614104
                                              Mark Rand
                                              Participant
                                                @markrand96270

                                                SY might not comply with the 18th edition (having got 15, 16 and 17 I've given up on keeping up to date), but it's been standard fitment for exposed flexible 415V cables to movable machine tools for decades. SWA is unsuitable for that use.

                                                There's generally no need for it in internal cables, but it works.

                                                PS:- electrons are colour blind…

                                                Edited By Mark Rand on 19/09/2022 08:41:40

                                                #614109
                                                Robert Atkinson 2
                                                Participant
                                                  @robertatkinson2

                                                  A couple of comments:

                                                  SY cable IS armoured. It is not "steel wire armoured" (SWA). SWA is a different class of cable.

                                                  SY cable is flexible (SWA is not)

                                                  While it is good practice to ground the braid in SY (and SC) cable, it is not technically necessary for electrical safety. This is because there are two layers of insulation between the conductors and the braid. These are functional (around the conductor) and basic (over the functional, under the braid. The clear outer layer adds another layer of protection against accidental contact with a live conductor.

                                                  The fact that SY cable comes with a Green/Yellow Protectice Earth (PE) conductor should make it clear that the brade is not intended for use as a protective ground.

                                                  Cable and wire does NOT have to be UKCA (or CE) marked. Made up assemblies like "cordsets" used for computers and the like do. In fact cable, as a component, should not be UKCA (or CE) marked as such a mark could be taken to mean a cordset made with it was compliant when it might not be.

                                                  Despite what the IEEE would like us to think, BS/EN 7671 is NOT a regulation. It is a standard. There is no legal requirement to comply with it (one exception, below). It is however the easy route to show compliance wiht the actual regulations (basically it has to be safe). The excepton is rented properties where somehow we have made it a legal requirement to comply with a commercial standard which is not good practice. That particular law is badly written becuase it specifies the 18th edition. so when the 19th comes out either the law will have to amended or work done to an old edition…

                                                  Robert G8RPI.

                                                  #614111
                                                  Pete Rimmer
                                                  Participant
                                                    @peterimmer30576

                                                    Actually SY cable should not utilise the braid as earth protection:

                                                    https://www.voltimum.co.uk/content/earthing-cable

                                                    #614112
                                                    Mike Poole
                                                    Participant
                                                      @mikepoole82104

                                                      I have known SY used in an application where it moved and the braid broke and pierced the insulation to the conductors. I think SY is intended to be used in static applications and not required to flex. In the car factory it was the standard cable for connecting static devices and many miles were used. In applications where regular movement was required it was not specified or used.

                                                      Mike

                                                      Edited By Mike Poole on 19/09/2022 10:13:05

                                                    Viewing 25 posts - 1 through 25 (of 40 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Home Forums Manual machine tools Topics

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up