        Hi All.

        Theb Danfoss type C10 220v coil starter and T 16 overload has finally given up the ghost after 40+ years of use. However it seems as though a replacement analogue unit is no longer available. can someone point me in the direction of an alternative please. preferably one that will involve the minimum of cable alts. I dont mind redoing the front panel and buttons but would like to keep the original door , guard and back gear safety switches.

        Many thanks

        Brian.

        #575771
        Emgee
        Participant
          @emgee

          Brian

          It should be possible to obtain a suitable replacement contactor and overload to replace the faulty unit/s so just a case of removing the old and fitting new.

          If the original stop and start buttons operated rods to push in contacts on the contactor and o/l then you may need to fit a new stop and start module hard wired to the contactor and overload.

          Emgee

          #575775
          Mike Poole
          Participant
            @mikepoole82104

            It could be economical to buy a direct online starter (DOL) and not use the case. You may need new buttons, a normally open (NO)start button and a normally closed (NC) stop button, usually green and red. Inverter drive supermarket list DOL 230v starters by WEG, you will need to choose the one with the correct overload range for your motor.
            Tool station list Starters by IMO and also individual contactors and overloads, rather pricier than the WEG units. To build a motor starter you will need a contactor with a 230V coil, typically it will have 3 normally open contacts (NO) for the load and a (NO)auxiliary for the control circuit, the auxiliary is often just a fourth contact rated the same as the load contacts on a small contactor but on very high power ones the auxiliary will be much smaller rated for control duty only. The overload module should match the contactor as they are designed to fit together but stand alone types are also available. A NO button to start and a NC button to stop is all you require apart from some suitable cable and a circuit diagram. Guard and door switches can be incorporated as well as any extra stop buttons or foot stops that you may desire. There is a choice of buttons available and I would choose a green start button that is flush or below the surrounding shroud, the stop would be red and you have a choice of a simple operator that is above the shroud or small or large mushrooms. If locating new components in the existing space is not possible then the complete starter in its own enclosure can be remotely mounted and just the control buttons connected from their existing position and motor cable rerouted or replaced.

            Mike

          Viewing 4 posts - 1 through 4 (of 4 total)
          • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

          Advert

          Latest Replies

          Home Forums Manual machine tools Topics

          Viewing 25 topics - 1 through 25 (of 25 total)
          Viewing 25 topics - 1 through 25 (of 25 total)

          View full reply list.

          Advert

          Newsletter Sign-up