Quote from the Green Book
10.13 Any loss of pressure shall be fully investigated. Slight loss from blanking plugs and fittings may be allowed. The boiler fittings should be examined for integrity, thread quality and dezincification to eliminate any risk of subsequent detachment.
10.14 Pressure loss which cannot be accounted for or which is at an unacceptable level shall lead to the test being declared a failure.
10.8 For all further hydraulic repeat tests, i.e. subsequent to the initial hydraulic shell test, the boiler shall be fitted with the working components attached to the boiler shell to prove the pressure and structural integrity of the interface and the boiler fittings. This includes the pressure gauge. If the gauge is not of the full range required by the test (1.5 x PW) it shall be disconnected and a blank fitted. On completion of the test (1.5 x PW) the blank shall be removed, the gauge shall be reconnected and a pressure applied equal to the full range of the pressure gauge. The pressure is to be applied for a sufficient length of time to prove the structural integrity of the gauge fitting.
10.9 If practical, the superheater should be included in the hydraulic repeat pressure test. This requires a blank to be fitted on the outlet of the superheater. It shall be removed on completion of the test and the pipe reconnected. The regulator shall be in the ‘Open’ position for the test. For superheaters the Boiler Inspector shall assess the testing requirement on an individual basis and annotate the Written Scheme of Examination accordingly.