      Hi everyone,

      I'm looking for some help we a 3 phase converter I've been given a while ago, and never used a 3 phase converter before I'm puzzled on how to set it up to run?

      I have a small horizontal mill which was on single phase and decided to buy a new 12hp 3 phrase motor to go with converter (the motor company helped to make sure I had the correct motor for the converter) so I can better control the cutting speed, instead of having to mess around with the rats nest of pulleys every time I wish to change speeds.

      My issue is i have no information/instructions on how to get the inverter to work or how to set the parameters? A electrician friend helped me with the wiring installation so that been done correctly.

      Would any kind more knowledge person be able to help please, I'm fairly new to the forum but I've managed to put some pictures in a album

      Many thanks in advance

      George

      Edited By George Jervis on 22/09/2018 11:50:39

      Advert
      #31975
      George Jervis
      Participant
        @georgejervis86082

        3 phase converter help needed please

        #372692
        Speedy Builder5
        Participant
          @speedybuilder5

          What sort of phrases did you want to convert – (Tongue in cheek)
          BobH

          #372696
          Martin Cargill
          Participant
            @martincargill50290

            A quick google found the manual I didn't download it but it will probably have a "quick start" guide. The manufacturer will have a technical helpline that should give you assistance with parameter issues.

            Martin.

            #372700
            not done it yet
            Participant
              @notdoneityet

              George,

              The first thing to do is check that the motor is wired for delta and not star. The VFD factory default settings should be good, as a starting point, to get running. Remote starting and stopping is usually a more advanced set up, as are individual trip settings for your particular circumstances.

              #372703
              George Jervis
              Participant
                @georgejervis86082

                Hi
                The motor company told me to change the jumpers to DELTA configuration as they were sold in star originally, so I’ve changed them to DELTA before wiring everything up
                George

                #372713
                David Jupp
                Participant
                  @davidjupp51506

                  Manual is available from Schneider

                  **LINK**

                  Not the most user friendly of manuals, but being a fairly old design there aren't many options to worry about. Unusually this device doesn't have run/stop buttons on the front, so switches of some kind will have to be wired.

                  #372856
                  George Jervis
                  Participant
                    @georgejervis86082

                    Hi
                    I’ve managed to print out a copy of the Manuel and followed it best I can but still no joy it seems like the parameters are locked and can’t be changed? So inputting the motor plate info can’t be done? I checked the wiring again today that’s okay. The motor is brand new from “the motor company” aka (TEC) which are about a miles ish from my home so no postage to worry about damage.
                    Has anyone got any ideas please

                    George

                    #372871
                    Gary Wooding
                    Participant
                      @garywooding25363

                      Are the parameters locked even though the L2A parameter shown on page 56 is set to Yes?

                      #372872
                      not done it yet
                      Participant
                        @notdoneityet

                        Two of my inverters, I think, have one particular program setting number which locks, or unlocks, the programming – to avoid individuals, on the shop floor, tampering with the settings. I think that setting could only be accessed, on one VFD, after the it was left unpowered for some time. I can’t remember the Schneider manual as I didn’t really need it – that VFD had failed, probably due to old age.

                        #372873
                        David Jupp
                        Participant
                          @davidjupp51506

                          p. 53 onwards of the manual covers parameters modification and gives some examples.

                          ItH should be set to nominal motor current (for thermal protection), take from motor plate.

                          bFr set to motor base frequency; 50 or 60 (almost certainly 50)

                          The setting method is very clunky, so read the examples carefully. ItH & bFr are both level 1 parameters.

                          You can define some preset speeds to call depending on switch positions. LSP, HSP, JOG, S3 S4.

                          All these are 'Level 1' parameters, so follow examples / flowchart for level 1.

                          Since you have a 0.37kW motor and a 0.37kW drive the factory default settings for motor should be reasonable – if in doubt you could perform a FCS (a level 2 parameter).

                          #372897
                          Martin Cargill
                          Participant
                            @martincargill50290

                            From your photos it looks like the drive is ready to go ( the RDY on the display). To give further assistance:

                            Can you photograph the wiring that you have going into the drive.

                            A photograph of a sketch of the wiring would also help.

                            Also a list of the parameters and what you have them set to would also help

                            Martin

                            #372907
                            George Jervis
                            Participant
                              @georgejervis86082

                              Hi everyone,
                              Thank you for the continued help I’ve managed to check and it’s set up to 50Hz and L2A is on YES as well, but still no joy?
                              One of the parameters say I have 235 to 236 volts going into the converter so I have enough voltage going in.
                              Knowing my luck, it’ll be something really simple lol (I hope)
                              George

                              #372908
                              John Rudd
                              Participant
                                @johnrudd16576

                                As Martin has said above, we need a diagram of how the inverter is wired, especially the stop/start and speed inputs.

                                Reading the manual, it looks like these inputs are missing hence the 'no go' Page 47…

                                The front panel controls seem lacking in functionality…

                                #372915
                                George Jervis
                                Participant
                                  @georgejervis86082

                                  Hi Martin,

                                  I've put some more pictures in a album of the wiring to the motor and converter

                                  The wiring I've used is 1.5mm2 sc 4 core

                                  Converter wiring as follows

                                  U is wire 3

                                  V = 2

                                  W=1

                                  E tm earth

                                  And the motor is wired too

                                  U1 is wire 3

                                  V1 is 2

                                  W1 is wire 1

                                  Earth is E

                                  I'll try and write what the parameters I have on the converter at the moment but this might not be on here until later or tomorrow morning.

                                  Many thanks again for the help

                                  George

                                  #372917
                                  David Jupp
                                  Participant
                                    @davidjupp51506

                                    What about the control wiring ? Nothing will work without that.

                                    #372922
                                    John Rudd
                                    Participant
                                      @johnrudd16576
                                      Posted by David Jupp on 23/09/2018 17:59:50:

                                      What about the control wiring ? Nothing will work without that.

                                      Err…like what I said above….George you need some more string….and leave the inverter settings alone for the time being…concentrate on getting the motor to turn first..

                                      #372926
                                      George Jervis
                                      Participant
                                        @georgejervis86082

                                        This is were I could have gone wrong ? Does this mean I have to have a separate on off switch?

                                        I had a few years ago a 3 phase converter on a large drill press that I just pressed the enter button for on or off and used the arrows up and down to increase or decrease the speed but I have sold that now. I had assumed that this 3 phase converter would be the same??

                                        George

                                        #372928
                                        John Rudd
                                        Participant
                                          @johnrudd16576

                                          George,

                                          Can you fit a short length of single core wire to connect LI1 and +24v together, then another wire to +10 and AI1 terminals? Then tull us what happens…Hopefully the motor runs at full speed..

                                          #372931
                                          George Jervis
                                          Participant
                                            @georgejervis86082

                                            I’ll have to try that tomorrow morning and I’ll let you know what
                                            happens, fingers crossed

                                            Thank again everyone for trying to figure this out
                                            George

                                            #372959
                                            Martin Cargill
                                            Participant
                                              @martincargill50290

                                              George.

                                              Don't do anything yet with regard to trying to start the motor. We need to know a bit more about how you have the motor wired. What you have shown so far is the power wiring, As John Rudd has pointed out the control side of the wiring is missing. What I'm not sure of just now is how you have connected the motor. Does the wiring run directly from the converter to the motor, or does it go through the original switchgear? Does the power supply to the converter go through the original switchgear or direct from the mains?

                                              Martin

                                              #372962
                                              George Jervis
                                              Participant
                                                @georgejervis86082

                                                Hi Martin,
                                                The converter is plugged straight into the house mains via a 13amp plug and the motor is wired directly to the converter with no switches inbetween.
                                                The original switch on the mill you may see isn’t connected to anything anymore.
                                                in my rush to get the 3 phase motor on I cut the wire to the single phase motor and and switch that was on the mill originally
                                                George

                                                #372963
                                                Martin Cargill
                                                Participant
                                                  @martincargill50290

                                                  George. That's fine, please continue to try the instructions that John Rudd gave you. My concern was that you had managed to include the old switchgear into the circuit, most convertors don't take too kindly to having their output switched by contactors.

                                                  Martin

                                                  #373044
                                                  George Jervis
                                                  Participant
                                                    @georgejervis86082

                                                    Hi everyone,
                                                    I’ve put some more pictures in my album to show were I’m up to.
                                                    I’ve been in touch with my electrician friend who gave me the it, and we’ve been slowly going through his list of things to try. There’s still no luck with it so far but thought I’d keep everyone updated as to how it’s going or if anybody else has any more input that can help
                                                    Thank
                                                    George

                                                    Edited By George Jervis on 24/09/2018 12:48:17

                                                    Edited By George Jervis on 24/09/2018 12:48:55

                                                    #373047
                                                    David Jupp
                                                    Participant
                                                      @davidjupp51506

                                                      The manual clearly shows (top of p47) that if you are not using an external 24V supply, you should common together LO+ and +24 to feed the switch inputs.