      An interesting article, but anyone considering building something similar should note that the author has used an XLR connector for the thermocouple instead of a proper thermocouple connector that should have been used.
      Dave Martin
        @davemartin29320
        #357956
          As I recall from my a-level physics lessons, the nature of any connections/interwiring doesn't actually matter as long as they are all at (practically) the same temperature as the cold junction.
          #357961
          Dave Martin
            @davemartin29320
            Sorry Neil, but I think it does matter, I haven't time to dig out my Physics/ElecEng degree text books to calculate it though.
            The article talks about "affordable precision" and "with great accuracy" – but then spoils it.
            Proper thermocouple connectors are probably no more expensive than the XLR connector used. No excuse not to use them.
            Also, re-reading the article, it describes using "thin gauge stranded wire for the thermocouple connections" – it should be the appropriate thermocouple material wires that are used to extend the thermocouple appropriately, not generic copper wire for both cores.
            #357964
            I.M. OUTAHERE
              @i-m-outahere
              For the dummies like me out there can you please explain why it matters ? I don't have a degree of any kind but like to learn so any info you have about this would be a worthy addition to the filing cabinet that resides between my ears !
              #357965
              Emgee
                @emgee
                Agree with Dave that any cables extending thermocouple's should be as specified by the manufacturer and they certainly won't be standard copper cables, used to buy mine from RS but that was many years ago.
                Emgee
                #357973
                  Posted by XD 351 on 15/06/2018 23:59:11:
                  This is a good introduction: **LINK**
                  http://enacademic.com/dic.nsf/enwiki/19021/Thermocouple
                  and the 'why it matters' is pretty much covered by the Measuring Circuit diagram and the 'Principle of operation' text.
                  If the thermocouple lead is extended with [say] twin copper wires, then the conector block will become the cold reference junction; regardless of the design intention of the measuring instrument.
                  In the Environmental Test House, we made our own thermocouples, simply by welding a junction on the end of a [sometimes very long] piece of 'extension wire' … The result is much more reliable.
                    Very educational this site, it would never have occurred to me that plugs & sockets might matter on a thermocouple. Nothing but good news because the proper plugs are cheaper than XLR.
                    Edited By SillyOldDuffer on 16/06/2018 09:13:12
                    #357985
                    Nige
                      @nige81730
                      I wonder what actual difference use of the 'proper plug' and cable would have made in this project. The device appears to do everything its designer wanted except that the achieved temperatures may or may not be exactly as he thinks he measured, but different by how much and will it make a difference. Could be the guy who built it knew full well that an XLR plug and thin stranded copper wire would work well enough for his application.
                      #357991
                      Dave Martin
                        @davemartin29320
                        You're right Nige, it will work, but not as well. The thermocouple effect – in which the genuine signal is very small – arises from dis-similar metals at a different temperature to the 'reference junction'. Every change of material, such as using the wrong wire, introduces at least one extra thermocouple which will bring an error. Using connectors, there will be several changes of material, and with plated pins, there may be a number of transitions. Wrong wire and wrong connector errors can introduce errors of maybe up to 10 degrees or more; and they won't be just fixed errors – each transition is a separate thermocouple, so depending on ambient and temperature inside the enclosure, the errors won't even be fixed.
                        #357992
                          So with a temp of 1000deg on a furnace does 10deg error really matter in this instance, probably not but may be an issue if heating a pendantwink 2
                          Also I expect the controller could be programmed to compensate for any errors if you had an accurate way to measure what that temp was.
                          #357996
                          fishy-steve
                            @fishy-steve
                            Posted by SillyOldDuffer on 16/06/2018 09:12:46:
                            You would have to buy the female facia mount too.
                            Might still be cheaper though. Haven't checked. 😉
                            Steve.
                            #357997
                            Andrew Tinsley
                              @andrewtinsley63637
                              Jason,
                              Why on earth bother trying to programme the PID controller to correct the error? I seriously doubt that one could anyway.
                              10 degrees is 10 degrees error that can be eliminated by using the correct connector, which is in fact cheaper than the specified connector! OK if you are measuring 1000 degrees it doesn't much matter, but if you are measuring a100 degrees it sure as hell does!! Once you have a PID controller, then who knows what you will be controlling in future?
                              #357998
                                Any other voltages generated by thermocouple effects will be:
                                1 symmetrical if the wiring for the routes in and out are the same, having no impact on the situation (Kirchoff's law.
                                The voltages around a circuit sum to zero).
                                2 The voltage across the thermocouple is generated across the portion of the sensor wires where a temperature gradient exists. It is negligible for any parts of the system at a uniform temperature.
                                Certainly for ultimate accuracy you need consistency and continuity of the connections.
                                However, it is not the temperature difference between the cold junction and the hot junction that creates the voltage, it's the temperature difference between the hot and cold parts of the thermocouple wires.
                                As variations in temperature beyond the kiln are likely to be negligible compared to the gradient inside and outside the kiln the impact on overall accuracy will be negligible as well.
                                #357999
                                  Yes I had to check a few facts using Google but I'm amazed how much I remember from 38 years ago!
                                  #358012
                                  Anonymous
                                    Irrespective of the thermal rights and wrongs of connector choice the use of XLR seems a bit odd. They're large and expensive. One of the few places they get used is in professional audio and broadcast equipment. Bizzarely on some OB equipment they're a "standard" for connecting external battery packs.
                                    Even if the use of an XLR has little effect I think a proper thermocouple connector would be better. They're cheaper, and a sensible design goal would be to eliminate the errors that are easy to do, and concentrate on those that aren't.
                                    #358013
                                    Robert Dodds
                                      @robertdodds43397
                                      A very timely article for me as I'm just upgrading the control of an enameling kiln.
                                      I bought much the same gear but as a kit, which came complete with a heatsink for the SSR. That raised the question of how much heat is being dissipated by the SSR. Reference to the web soon indicated that it was typically 1.5 watts per amp of current through the device so your 2Kw kettle sends about 15w out of the SSR.
                                      I think that is a bit too much for a sealed plastic box to withstand for longer periods such as with kilns etc.
                                      There is no mention of a heatsink in the article so am I being over cautious mounting mine with heatsink in a ventilated steel enclosure?
                                      Bob D
                                      #358023
                                      Ian P
                                        @ianp
                                        Posted by Robert Dodds on 16/06/2018 12:15:42:
                                        Bob D
                                        Well the heat produced by the SSR will still be inside the enclosure whether there is a heatsink or not. In practice though the simplest is to mount the SSR on an internal surface of the enclosure. Sttel is not the best heatsink material but the losses in the SSR that cause it to heat up are only really when it is in the 'ON' state. Depending on the duty cycle the final heating effect will probably be insignificant. I have used hundreds of controllers and SSRs, rarely if ever done any calculations and usually just mounted them on a convenient surface. I dont recall any ever getting noticeably hot or failing.
                                        Ian P
                                        #358029
                                          Posted by Andrew Johnston on 16/06/2018 12:11:06:
                                          I use XLR for my homebrew astro kit. robust, designed to be repeatedly plugged and unplugged and most of all, positively locking.
                                          #358073
                                          Nige
                                            @nige81730
                                            How many of us go to the junk box first to find components we need.. Want a two wire connection, Mmmm let me see, what have we here, a bit of chocolate block, Nah not easy to plug/unplug, 5 pin DIN plug, damn, would be ok if I had a socket for it, oh here we go, a 3 pin XLR plug AND a panel mount socket, jobs a good un
                                            #358081
                                            Muzzer
                                              @muzzer
                                              As Neil says, it is simply necessary to ensure that the pairs of connector pins at each change of wiring are at the same temperature. That way, any thermocouple voltage induced across each set of contacts between dissimilar metals is automatically nulled by an equal and opposite one on the complementary connection. That goes for the contact between the back of the connector and any wiring, as well as the contacts between mating connector contacts themselves.
                                              If you look at the "proper" thermocouple connectors, you my be otherwise puzzled to discover that both contacts are made of the same material and plating, despite the thermocouple itself being composed of different metals. And if you look beyond the thermocouple probes themselves where they are integrated into "proper" industrial systems, you may be puzzled to see they have just used "normal" copper wiring. Nothing wrong with that at all.
                                              You can solder t/c junctions (with care) instead of spot welding them. And of course they work "correctly" from a thermoelectric point of view.
                                              As for whether XLR connectors are appropriate, it's mainly a question of whether they are able to produce a consistent, low resistance contact over the lifetime of the application. I don't know the answer to that but I'd be surprised if they weren't OK. Assuming they are from a reputable manufacturer.
                                              Murray
                                              #358083
                                                Posted by Nige on 16/06/2018 16:53:15:
                                                That's exactly why my Rotary Table Indexer uses a 5 pin DIN plug & socket to power the stepping motor. It's an awful bodge, intended to be temporary and never fixed. It's one of my shameful secrets.
                                                A good reason not mentioned for using proper connectors is that some sensors come pre-fitted with them. Not having to rewire to match an XLR would save a few minutes work.
                                                I think Dave's corrections are useful, but don't think the article was spoilt by the omission. Sometimes authors can't win. If he says he used XLR connectors in his build, some might take that as an essential instruction. I reckon Nige is right: XLR was used because it was handy.
                                                Dave Martin
                                                  @davemartin29320
                                                  Posted by Muzzer on 16/06/2018 18:09:37:
                                                  …..If you look at the "proper" thermocouple connectors, you my be otherwise puzzled to discover that both contacts are made of the same material and plating, despite the thermocouple itself being composed of different metals. ….
                                                  Sorry Muzzer, but not so. That's why, even in the same form factor, you have a range of connectors which are appropriate for E, J. K etc. – they use appropriate connection pins or plating. e.g.: http://www.precision-measurements.com/pdf/connector-systems-for-thermocouples.pdf
                                                  (Edit: corrected link)
                                                  Edited By Dave Martin on 16/06/2018 18:27:19
                                                  #358085
                                                    Another useful datasheet here: **LINK**
                                                    https://docs-emea.rs-online.com/webdocs/15bb/0900766b815bb539.pdf
                                                    Edited By Michael Gilligan on 16/06/2018 18:33:14
                                                    #358086
                                                    Dave Martin
                                                      @davemartin29320
                                                      and here are two RS data sheets that list the contact materials used for different types of thermocouple
                                                      from which:
                                                      [quote]
                                                        All THERMOCOUPLE connectors use true thermocouple alloys for optimum accuracy, Except for Type R, S & B which use compensating alloys.
                                                        Thermocouple Pins
                                                        Type /  ‘+’ Positive Pin  /  ‘-‘ Negative Pin
                                                        J  /  Iron  /  Copper Nickel
                                                        K  /  Nickel Chromium  /  Nickel Alloy
                                                        T  /  Copper /  Copper Nickel
                                                        E  /  Nickel Chromium  /  Copper Nickel
                                                        N  /  Nickel – Chromium – Silicon  /  Nickel Silicon
                                                        R  /  Copper  /  Copper Alloy
                                                        S  /  Copper  /  Copper Alloy
                                                      [/quote]
                                                      (Edit: – table format disappeared so separate columns with /  – crossposted with MichaelG at the same time!)
                                                      Edited By Dave Martin on 16/06/2018 18:42:37